What size main vents do I need?
fab4ever77
Member Posts: 8
New gas boiler (Burnham IN4), one header that splits to both sides of the house. Each main line is about 30 feet (one is 34 ft the other is 26 ft) of 2" pipe from the boiler to the main vent (so 60 feet total when including both sides).
What size main vents should I have at the end of these lines?
I was planning on buying a Gorton's #1 or #2.
Is there any advantage to having "oversized" main vents (I'm guessing the #2 is just slightly oversized for my unit)?
What size main vents should I have at the end of these lines?
I was planning on buying a Gorton's #1 or #2.
Is there any advantage to having "oversized" main vents (I'm guessing the #2 is just slightly oversized for my unit)?
0
Comments
-
I'm running five Gorton #1's on a 29' 2" main.
If I was you and you have the clearance I'd do a minimum of a single Gorton #2 per main.
Can you share some pictures of the boiler and it's piping with the forum?
Single pipe quasi-vapor system. Typical operating pressure 0.14 - 0.43 oz. EcoSteam ES-20 Advanced Control for Residential Steam boilers. Rectorseal Steamaster water treatment0 -
This is for a 1200 sq. ft house, 2 floors0
-
The rule of thumb around here is 1 Gorton #2 vent for each 20' of 2" pipe. So by that rule Chris's recommendation should be considered a bare minimum in all honesty. You can't really "over vent" your mains, but there is a point of diminishing returns. My mains are much shorter than yours and I am running 3 Gorton #1 on each (I can't fit a #2 or I would have them). For reference 3 #1 vents is close in capacity to a #2.0
-
My recommendation was "I'd do a minimum of a single Gorton #2 per main" So yes, it was minimum.KC_Jones said:The rule of thumb around here is 1 Gorton #2 vent for each 20' of 2" pipe. So by that rule Chris's recommendation should be considered a bare minimum in all honesty. You can't really "over vent" your mains, but there is a point of diminishing returns. My mains are much shorter than yours and I am running 3 Gorton #1 on each (I can't fit a #2 or I would have them). For reference 3 #1 vents is close in capacity to a #2.
Single pipe quasi-vapor system. Typical operating pressure 0.14 - 0.43 oz. EcoSteam ES-20 Advanced Control for Residential Steam boilers. Rectorseal Steamaster water treatment0 -
Sorry Chris I was just restating what you said. Wasn't trying to present it as a disagreement with you.0
-
What exactly will faster venting do for me? Should I do a Gorton's 1 and 2 on each side? If I0
-
Faster venting gets the steam available to the radiators faster. It also allows you to balance the radiators more easily. Think of it this way if you speed the steam to the radiators by 2 minutes then that's 2 minutes of fuel you have saved....on ever cycle. On a cold day 1 cycle per hour, 2 minutes per cycle 48 minutes of gas saved in one day. And then there is the added comfort. On a one pipe system it's all about the venting.0
-
If you can get one Gorton #2 and two Gorton #1's on each main, that will give you max venting. Two Gorton #2's will work great also and may be about the same cost as one Gorton #2 and two #1's.fab4ever77 said:What exactly will faster venting do for me? Should I do a Gorton's 1 and 2 on each side? If I
0 -
When you look at the cost of an antler full of Gorton #2's, a number of possibilities begin to look affordable.
Belimo's HTCCV is rated for 15 PSI of steam and comes in sizes ranging from a Cv of 0.29 to 28.0
Categories
- All Categories
- 86.2K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 52 Biomass
- 422 Carbon Monoxide Awareness
- 89 Chimneys & Flues
- 2K Domestic Hot Water
- 5.3K Gas Heating
- 99 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 910 Plumbing
- 6K Radiant Heating
- 380 Solar
- 14.8K Strictly Steam
- 3.3K Thermostats and Controls
- 53 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements