Venting of mid efficiency via chimney
Stenty
Member Posts: 74
Hello,
The current water heater is a 20yo gas fired tank atmospheric vented into a masonry chimney with single wall 26ga 3" pipe. Its making those wonderful gurgling sounds whenever a faucet is opened.
I'm looking to replace it with something with a higher efficiency but not necessarily a condensing unit.
Maybe a mid efficiency tank or tankless.
I looked at the Rheem EcoSense direct vent but the venting accessories are all double wall steel and I'm assuming that its a coaxial setup where supply air is brought in via that piping. I wouldn't be able to support the piping every 4' as required in the instruction so that's a no go.
Any suggestions?
Mid or high efficiency, masonry chimney vented, tank or tankless.
The current water heater is a 20yo gas fired tank atmospheric vented into a masonry chimney with single wall 26ga 3" pipe. Its making those wonderful gurgling sounds whenever a faucet is opened.
I'm looking to replace it with something with a higher efficiency but not necessarily a condensing unit.
Maybe a mid efficiency tank or tankless.
I looked at the Rheem EcoSense direct vent but the venting accessories are all double wall steel and I'm assuming that its a coaxial setup where supply air is brought in via that piping. I wouldn't be able to support the piping every 4' as required in the instruction so that's a no go.
Any suggestions?
Mid or high efficiency, masonry chimney vented, tank or tankless.
0
Comments
-
Any utility rebates available? How hard is the water, and what kind of chloride levels?0
-
Municipal water. There is very little scale issues and it tastes pretty good, no sense of chlorine in the taste of it.0
-
The Noritz NR981-SV-NG has single wall venting.0
-
I would suggest a condensing TWH with PP flexible venting. Installs in the existing chimney in about an hour, costs far less than stainless vent material.0
-
Would the upfront costs of a condensing unit outweigh the cost of SS vents?
Would a condensing unit also require piping for outside air?0 -
What other units are venting into that chimney?All Steamed Up, Inc.
Towson, MD, USA
Steam, Vapor & Hot-Water Heating Specialists
Oil & Gas Burner Service
Consulting0 -
No other appliances.0
-
That would let you do pretty much whatever you want, within the limits of safety. It's possible, as others have stated, to use the chimney as a chase for a concentric venting system. You want to avoid venting an appliance directly into the chimney that is so small it doesn't create proper draft, allows the exhaust gases to condense in the chimney, or both.
Whatever you do, avoid the use of PVC pipe for venting combustion appliances. Polypropylene (PP) or stainless steel are the way to go- they are UL listed for venting combustion appliances whereas PVC/CPVC is not. Yes, we see a lot of PVC combustion venting, but that doesn't mean it's the right way to go.All Steamed Up, Inc.
Towson, MD, USA
Steam, Vapor & Hot-Water Heating Specialists
Oil & Gas Burner Service
Consulting1 -
The Noritz NR981-SV is listed as Category III.
The Polypro Duravent pipe is listed a Category II and IV. Does that qualify it for Category III ? I don't know enough about the categories.
I once bought aluminum flue liner from my supply house for a gas boiler0 -
The Noritz NR981-SV is non-condensing.
Category II
An appliance that operates with negative static pressure in the vent and a temperature that is low enough to cause excessive condensation in the vent.
Category III
An appliance that operates with positive static pressure in the vent and a temperature that is high enough to avoid condensation in vent.
Category IV
An appliance that operates with positive static pressure in the vent and a temperature that is low enough to
cause excessive condensation in the vent.0 -
Right, so it needs stainless venting.0
-
What about lining the chimney with the appropriate size liner and installing one of these guys?
http://www.supplyhouse.com/Bradford-White-RG2D50S6N-50-Gallon-40000-BTU-Defender-Safety-System-Damper-Atmos-Vent-High-EF-Energy-Saver-Residential-Water-Heater-Nat-Gas
I'm suggesting this due to simplicity and silence. A standard atmospheric would be the cheapest, but I hate the pilot and all of that heat always going up the flue.
Single pipe quasi-vapor system. Typical operating pressure 0.14 - 0.43 oz. EcoSteam ES-20 Advanced Control for Residential Steam boilers. Rectorseal Steamaster water treatment0 -
LANGAN'S PLUMBING & HEATING LLC
Considerate People, Considerate Service, Consider It Done!
732-751-1560
email: langansph@yahoo.com
www.langansplumbing.com0
Categories
- All Categories
- 86.2K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 52 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 99 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 913 Plumbing
- 6K Radiant Heating
- 380 Solar
- 14.8K Strictly Steam
- 3.3K Thermostats and Controls
- 53 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements