adding basement hot water heating loop to burnham mega steam mst396 using domestic hot water coil
Options
charlie_22
Member Posts: 18
Want to add a basement hot water heating loop in my basement last year I installed a mst 396 mega steam boiler I have the optional hot water coil thinking about using it for heating loop what do you guys think any sugestions are greatly appreciated
0
Comments
-
only use it if you DO NOT USE IT FOR DOMESTIC HOT WATER!!!!!!!
It will also need all the trim ones uses for a hot water boiler. Water feeder, expansion tank, PRESSURE RELIEF VALVE, and air separator.Cost is what you spend , value is what you get.
cell # 413-841-6726
https://heatinghelp.com/find-a-contractor/detail/charles-garrity-plumbing-and-heating0 -
I have a ao smith vertex hot water heater for domestic hot water thanks for the advice0