modine hydronic unit heaters
smp74
Member Posts: 61
On a new system I requested that one be installed for my basement zone. Installer spec'd a 18k btu unit (HC18). It looks nice, but the rating is based on 2.5 PSI steam. It looks like with my mod-con boiler, output will be more like on the order of 5k - 10k btu at 140-180F. This is in a 800 sq ft basement, all open, mostly below grade. I fear that it won't keep up or have any room for recovery.
I'm looking at having it swapped out to a Modine HHD-30. This looks like it is designed for residential installations and can work properly with lower supply temps due to much larger heat exchanger. It also has a much quieter fan.
Does anyone have experience with the HHD-30 unit or have any advice as to the actual performance I can expect from the HC18?
I'm looking at having it swapped out to a Modine HHD-30. This looks like it is designed for residential installations and can work properly with lower supply temps due to much larger heat exchanger. It also has a much quieter fan.
Does anyone have experience with the HHD-30 unit or have any advice as to the actual performance I can expect from the HC18?
0
Comments
-
What is the heat loss of that basement space?All Steamed Up, Inc.
Towson, MD, USA
Steam, Vapor & Hot-Water Heating Specialists
Oil & Gas Burner Service
Consulting0 -
The slantfin calculator has it at about 15k @ 0F (southeast MA).0
-
The HC-18 won't do it. Not familiar with the HHD-30, but it has enough capacity to work in your system, so unless a red flag pops up somewhere I'd say go for it.All Steamed Up, Inc.
Towson, MD, USA
Steam, Vapor & Hot-Water Heating Specialists
Oil & Gas Burner Service
Consulting0 -
Thanks Steamhead. I'll see how far I can get with the installer on this. It is quite a bit wider than the HC18 unit, but there is plenty of space to mount it.0
-
That thing is an ugly monster . is the basement finished or like a shop / storage area ?
You should look into Smiths Environmental PSU40 . @ 130* it'll give you 14,204 and at 140* , 17,000 . Quiet too .
http://smithsenvironmental.com/products/profile-fan-convector/You didn't get what you didn't pay for and it will never be what you thought it would .
Langans Plumbing & Heating LLC
732-751-1560
Serving most of New Jersey, Eastern Pa .
Consultation, Design & Installation anywhere
Rich McGrath 732-581-38331 -
The high efficiency , low temp ratings are hereYou didn't get what you didn't pay for and it will never be what you thought it would .
Langans Plumbing & Heating LLC
732-751-1560
Serving most of New Jersey, Eastern Pa .
Consultation, Design & Installation anywhere
Rich McGrath 732-581-38330 -
Yep, the Modine is ugly, no doubt. The basement is, and will remain, unfinished as a workshop / storage. It's too small to start walling it off. The Smith unit does look nice, thank you for that option. It would, however take up wall space which may be an issue for my shelving and workbench. I'll try to remember to take a picture of the current setup for further eval and post here.0
-
If a fast warm up is one of the requirements, no question a forced convector is king.
Maybe look into a kickspace type heater, or two in a wall cabinet, they are much quieter.
Or a small air handler, anything with a squirrel cage blower will be much quieter.Bob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream0 -
Fast warm up is definitely a factor. I do not intend to keep the basement zone on all the time. That HHD30 unit does have a squirrel cage blower setup. Two wall mount unit heaters would be nice as well, but space is still an issue.0
Categories
- All Categories
- 86.5K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 423 Carbon Monoxide Awareness
- 96 Chimneys & Flues
- 2K Domestic Hot Water
- 5.5K Gas Heating
- 101 Geothermal
- 156 Indoor-Air Quality
- 3.5K Oil Heating
- 64 Pipe Deterioration
- 928 Plumbing
- 6.1K Radiant Heating
- 384 Solar
- 15.1K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 48 Job Opportunities
- 17 Recall Announcements