Have a job to convert from oil to gas. This is a job with new oil furnace, Oil hot water heater heating basement baseboard system and electric hot water heater.
New system, gas h/w boiler, IWH and hydro-coil for duct system.
Question, have you ever done hydro-coil and A/C coil both on the supply side of the fan? I realize normally the a/c is on the inlet of the fan and the hydro-coil on discharge side of the fan. No room to move the A/C coil to return.
The blower is an ECM motor.

Comments

  • NJ, Designer
    NJ, Designer Member Posts: 53
    Please explain your question a little better
  • Bob Bona_4
    Bob Bona_4 Member Posts: 2,083
    I'd think you'd want a external slab cased evap for this, then the HW coil down the line. Sounds like you're keeping existing air handler. Was it solely electric coils and a blower?
  • Rich_49
    Rich_49 Member Posts: 2,768
    A single coil which does heating and cooling is not something exotic .
    You didn't get what you didn't pay for and it will never be what you thought it would .
    Langans Plumbing & Heating LLC
    732-751-1560
    Serving most of New Jersey, Eastern Pa .
    Consultation, Design & Installation anywhere
    Rich McGrath 732-581-3833
  • njtommy
    njtommy Member Posts: 1,105
    I think what he means is this confugeration

    Hot water coil top
    DX coil middle
    blower/ IDF on bottom

    I believe he is worried about freezing the coil. Not really a big deal just install a freeze Stat on the system and set it around 35-40 degrees.
  • Jason_13
    Jason_13 Member Posts: 304
    Sorry for not being too clear.
    My concern is as follows. I am used to having the A/C coil on the return side of the blower and the H/W coil on the supply. This job will be set up as follows.
    Return from ceiling to a return air box. Blower cabinet on the supply side of air box. Exiting the supply side of the blower see's the H/W coil first and than the A/C coil. My concern is too much resistance on the supply and very little on the return.
  • njtommy
    njtommy Member Posts: 1,105
    What manufacturer are you looking at?
    What's is that static pressure of the current system?
    What is the static pressure drop of the hot water coil?
  • Bob Bona_4
    Bob Bona_4 Member Posts: 2,083
    I would do the evap then the hydronic coil. Just me. Done every single day with the Trane Hyperion/American Standard TAM7 and 8's with the hw coil kit. Nice stuff.
    njtommy
  • njtommy
    njtommy Member Posts: 1,105
    Off topic, @Bob Bona the Trane Tam7 nicest AHU I've ever seen. Solid as a rock
    Bob Bona_4
  • Bob Bona_4
    Bob Bona_4 Member Posts: 2,083
    I like the push thru design, I offer the TAM4 for "budget" situations.