We are in the beginning process of filling the hydronic heating system of a 5 story building. In order to hopefully speed up the task I have initiated the fill. My theory is to apply enough water pressure to to get the basement loop filled and possibly partially up into the risers of the 1st floor so we can check packing nuts on unit shut off valves.
My question is if the gauges on the boilers and pumps read 16 psig is the water column up @ 32 feet. (Theory: 1 psig raises water 2.30 feet.)? Or am I looking at head pressure of the column and the water is only up @7 feet? (Theory: 16 psig multiplied by .434 = @ 7 feet)
Thanks,
My question is if the gauges on the boilers and pumps read 16 psig is the water column up @ 32 feet. (Theory: 1 psig raises water 2.30 feet.)? Or am I looking at head pressure of the column and the water is only up @7 feet? (Theory: 16 psig multiplied by .434 = @ 7 feet)
Thanks,
0
Comments
-
Your static height of water at 16psi is 36.96 feet. (16psi x 2.31).Contact John "JohnNY" Cataneo, NYC Master Plumber, Lic 1784
Consulting & Troubleshooting
Heating in NYC or NJ.
Classes0 -
If the goal is to fill and purge a large zone or loop, you need the fill pressure noted as well as sufficient flow. Or break the system to small zones or sections and purge one at a time.
Similar to geo loop fields, installers that fill and purge the entire loop field use a high flow fill pump, like a high gpm pool pump or more. A 1/2" fill line will only supply so much flow.Bob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream0 -
If you have isolation valves on the boiler(s) and expansion tank, you can crank up the system pressure (think 50+ PSI) which makes purging a lot easier.0
-
Most of the manufacturers offer 3/4 fill valves. Sometimes referred to as commercial fill valves.
This one will flow around 9 gpm, about twice the gpm of the 1/2" version.Bob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream2 -
You might want to put a gauge on the top floor, then use the fill to pressurize the system. See if it holds pressure. If it's really bad, you might want to switch to compressed air. I'd rather chase an air leak than water.0
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 917 Plumbing
- 6.1K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements