mixing valve
Comments
-
-
-
what pipe size?0
-
-
How hard is the water?0
-
4 " DISCHARGE PIPING. EXISTING TOUR- ANDERSON ENGINEERED SOPHISTICATED PRODUCT. WIRING HARNESS BROKEN BEYOND REPAIR & PRODUCT OBSOLETE , MAYBE 15 YEARS OLD. REPLACEMENT PARTS NOT AVAILABLE. LOOKING AT SIMILAR 2 " VALVE BY HEAT-TIMER0
-
-
HOLBY WAS ALWAYS MY CHOICE SINCE 1962 BUT THESE NEW VALVES SEEM TO OFFER NEW TECHNOLOGY THAT IS MORE UP TO DATE. OPINIONS WELCOMED & WANTED.0
-
The Heat Timer ETV sure seems like a cool unit. I wish they were around twenty years ago when I had the maintenance contract on a nursing home, although the biggest problem there were cross connections in the ancient shower valves and low flow conditions. It looks like that unit handles low flow well. Have you used them SWEI?0
-
-
Not to discuss pricing, but about how much more are they than the above mentioned valves? Just ballpark. They definitely look like much less of a headache than dialing in a thermostatic.0
-
-
Never size mixing valve to pipe size. Actually pipe size has nothing to do with mixing valve sizing. Size it to the load and pressure drop. I like Holby, they are very good, Tour and Anderson is good as well but requires certain piping set up on domestic hot water return line and constant flow through the valve to be precise in controlling of water temperature. And I love Honeywell MX valves.Gennady Tsakh
Absolute Mechanical Co. Inc.1 -
IF YOU GO WITH SUGGESTED PIPING DIAGRAMS AS I " ALWAYS " DO , YOU CAN'T GO WRONG. IF YOU CHOOSE TO COWBOY IT YOU GET WHAT YOU DESERVE, A GARBAGE JOB, VOID WARRANTIES AND LABELED " SAP ". CASE CLOSED.0
-
What are you referring to?
0 -
MR. GENNADY'S POST, OF COURSE. REGARDING PIPE SIZING, JONNY0
-
I would hesitate to call his methods of cowboying it if that is what you are referring to.What is wrong with his method?0
-
What Gennady is saying is correct, any valve, check, zone, mixing, etc, should be sized as close as possible to the flow rate it will be used at.
This is especially critical with mix and balance valves that depend on the flow rate to accurately and sometimes safely in the case of DHW thermostatic valves, do their job. Valve authority is the term used that shows or allows a valve to do it's job.
Swing check valves are also sensitive to flow rate, if over-sized the check flaps in the breeze, or fluid flow Although swing checks really don't have a place in hydronics. They depend on a delta P to close and seal properly.
True you should follow the manufacturers piping suggestions, again this is critical with mix valves and recirc pumps on DHW.
Sizing the valve correctly really isn't always an installation manual detail, per say. The valve selection should be correct before the installation takes place, spec sheets and submittals should have all the sizing details. Or consult with the factory, or a knowledgeable engineer. In my opinion.Bob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream1 -
I would go with hot water fixture list first, (not quantity of apartments), then determine what kind of building it is, get max possible demand, GPM. Then how high is top fixture to determine static pressure drop, what is length of the longest run from mixing valve to the farthest fixture to determine dynamic pressure drop. Knowing pressure drop (Cv) through mixing valve or using diagramm in the valve manual, street water pressure and possible max demand I would choose the valve.
Pipe size around the mixing valve is not a factor here.
I don't see where I was a cowboy here.
And if properly sized and installed any valve would work. If procedure of sizing is not followed, any valve would not perform well.Gennady Tsakh
Absolute Mechanical Co. Inc.1 -
Well stated.gennady said:I would go with hot water fixture list first, (not quantity of apartments), then determine what kind of building it is, get max possible demand, GPM. Then how high is top fixture to determine static pressure drop, what is length of the longest run from mixing valve to the farthest fixture to determine dynamic pressure drop. Knowing pressure drop (Cv) through mixing valve or using diagramm in the valve manual, street water pressure and possible max demand I would choose the valve.
Pipe size around the mixing valve is not a factor here.
I don't see where I was a cowboy here.
And if properly sized and installed any valve would work. If procedure of sizing is not followed, any valve would not perform well.
Now in some cases manufactures state some un-realistic flow numbers, I feel.
I see 3 Cv thermostatic mix valves with max. flow rates of 20 gpm or higher listed in the spec sheet!
Yes, the valve could flow that many gpm, probably with some noise complaints, but the ability to accurately adjust the temperature slips away.
One design engineer I know suggest 1- 1.5 bar (14- 20 psi) working ∆P across the valve. Flowing 20 gpm through a 3 Cv valve would look like this.
Oversizing a thermostatic valve will cause problems at very low flow conditions, look at the minimum flow on the spec. on large, high and low potential flows, a mixing station that couples multiple valves, sometimes called Hi-Low is a better option, or a motorized type valve, perhaps.
Bob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream0 -
I have not used the Heat-Timer version, but when I looked into it recently, I found out their 1-1/2" model (Cv = 29) would cost us about $200 more than a Symmons 7-1000 (Cv = 22.3) and probably eliminate 95% of the maintenance -- not to mention the >50% cost for "element" replacements on the thermostatic every few years.RobG said:The Heat Timer ETV sure seems like a cool unit. I wish they were around twenty years ago when I had the maintenance contract on a nursing home, although the biggest problem there were cross connections in the ancient shower valves and low flow conditions. It looks like that unit handles low flow well. Have you used them SWEI?
We are installing the first prototype of our own electronic tempering valve based on a similar NSF-listed stainless globe valve this weekend. We've paired it with some serious DDC smarts that also manage the indirect temp, boiler modulation, and respond to demand signals from building occupancy, laundry loads, and incoming cold water temp. I expect it will take about a year to optimize, but we expect to learn a lot in the process.2 -
-
Most of the TMV makers publish sizing charts, which make it difficult to compare products. I had to convert a number of them into Cv just to see what was what. Caleffi is one of very few who put the Cv on the front page of the spec sheet.0
-
Bob, turn your high beams down Your cap lock must be on?bob young said:JONNY, I WAS TOTALLY IN AGREEMENT WITH MR. GENNADY AND MY MAN HOT ROD IS ALWAYS ON THE MONEY. THATS A FACT. THANX MUCH FOR THE EXPERT ADVICE, GENTS. I APPRECIATE IT VERY MUCH. YOU GUYS ARE THE BEST. BOB NYC
Bob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream2 -
sorry hot rod, i read ya loud & clear !!!0
Categories
- All Categories
- 86.5K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 423 Carbon Monoxide Awareness
- 96 Chimneys & Flues
- 2K Domestic Hot Water
- 5.5K Gas Heating
- 101 Geothermal
- 156 Indoor-Air Quality
- 3.5K Oil Heating
- 64 Pipe Deterioration
- 928 Plumbing
- 6.1K Radiant Heating
- 384 Solar
- 15.1K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 42 Industry Classes
- 48 Job Opportunities
- 17 Recall Announcements