Latest Steam Boiler Install
JStar
Member Posts: 2,752
Replaced an old WM oil-fired boiler with a new Peerless 64-10 in Montclair, NJ. The old boiler was piped correctly, but only had a 3" header, trying to move 515MBTUH+. We installed a 5" drop header with two 3" boiler risers. Added a Vaporstat and 2-stage GCV. The system is a mix of one-pipe radiators throughout the house, and two-pipe indirect heaters in the basement. The wet returns were 30" high off the floor, so we kept our Gifford Loop above that level to keep them wet. The old boiler sections looked like they were never cleaned, and the soot had turned into concrete. Of course, the service tags were always filled out.
0
Comments
-
What was the old one- 76 or 78 series maybe?All Steamed Up, Inc.
Towson, MD, USA
Steam, Vapor & Hot-Water Heating Specialists
Oil & Gas Burner Service
Consulting0 -
-
Those 80-series boilers run nicely with gas burners. But like anything, if they're neglected enough, they won't last. And the 4-80 requires a minimum 4-inch header- only the 3-80 can get away with a 3-incher.
Nice work.
All Steamed Up, Inc.
Towson, MD, USA
Steam, Vapor & Hot-Water Heating Specialists
Oil & Gas Burner Service
Consulting0 -
-
How many times did you trip over that wet return running across that entryway?0
-
Luckly, that was not our entrance. Instead the basement doors were about 50 ft away, around two corners, and through a doorway where an indirect heater had previously fallen off its hangers on the ceiling.0
-
Sounds like fun!JStar said:Luckly, that was not our entrance. Instead the basement doors were about 50 ft away, around two corners, and through a doorway where an indirect heater had previously fallen off its hangers on the ceiling.
At least it wasn't a hoarders house by the looks of it.0 -
-
Do you have a company you use to replace rickety stairs or do you leave that to the client? I've got a carpenter that I will refer the HO to but it is between them and him. Some of those old stairs I will refuse to bring a boiler up nor down.JStar said:Of course, the bigger the boiler, the further the boiler room is from the basement entrance, and the more narrow the stairway is.
0 -
We don't at the moment. Sometimes we'll offer a price to sure up the stairs ourselves since we do some handyman style work. I had an instance at another company where my helper convinced me that he could handle the top of the hand truck. We got to the first landing on the stairs, and the boiler dropped straight through to the floor. I don't even remember how I jumped out of the way.0
-
Another great looking job!
Looking at the first new boiler picture, the steam main on the left appears to be counterflow for the first 3-4' before the 90. How far could that go before turning into parallel flow without causing a problem?
Not being critical, just that there are a couple of situations I know of that might get re-piped in the future and there is about that horizontal distance before reaching the high point of the steam mains. They are parallel flow for the rest of the main. Reusing that existing portion of main would save a lot of grief and probably pain.
Thanks.
0 -
My rule is that the pitch can go either way as long as it's before the first radiator run-out.0
-
Understood; no radiator condensate should flow back into the header, only steam main drip and that should be very little especially if the main is insulated.
So consider that as an extension of the vertical main riser off of the header?? Just don't leave it flat to pool water.
See why you should stay in the field to direct/advise newbies like me? I would have pulled both arms out of the sockets and probably cut up floor joists trying to "correct" that slope.
Thanks again.0 -
Could you tell be about the 2 stage gas valve. My local Peerless rep is telling me it should not be done on this boiler. Does it have 2 gas trains?
There was an error rendering this rich post.
0 -
JStar.........Why is the Hartford loop so high?0
-
Paul48 said:
JStar.........Why is the Hartford loop so high?
JStar said:The wet returns were 30" high off the floor, so we kept our Gifford Loop above that level to keep them wet.
All Steamed Up, Inc.
Towson, MD, USA
Steam, Vapor & Hot-Water Heating Specialists
Oil & Gas Burner Service
Consulting0 -
Sorry....I missed that.0
-
Love that header!!Dave in Quad Cities, America
Weil-McLain 680 with Riello 2-stage burner, December 2012. Firing rate=375MBH Low, 690MBH Hi.
System = Early Dunham 2-pipe Vacuo-Vapor (inlet and outlet both at bottom of radiators) Traps are Dunham #2 rebuilt w. Barnes-Jones Cage Units, Dunham-Bush 1E, Mepco 1E, and Armstrong TS-2. All valves haveTunstall orifices sized at 8 oz.
Current connected load EDR= 1,259 sq ft, Original system EDR = 2,100 sq ft Vaporstat, 13 oz cutout, 4 oz cutin - Temp. control Tekmar 279.
http://grandviewdavenport.com0 -
Are those cast iron fittings as usual Joe?
Beautiful work.
Single pipe quasi-vapor system. Typical operating pressure 0.14 - 0.43 oz. EcoSteam ES-20 Advanced Control for Residential Steam boilers. Rectorseal Steamaster water treatment0 -
-
-
Categories
- All Categories
- 86.2K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 52 Biomass
- 422 Carbon Monoxide Awareness
- 89 Chimneys & Flues
- 2K Domestic Hot Water
- 5.3K Gas Heating
- 99 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 910 Plumbing
- 6K Radiant Heating
- 380 Solar
- 14.8K Strictly Steam
- 3.3K Thermostats and Controls
- 53 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements