Lochinvar WHN combustion analysis
Steve Minnich
Member Posts: 2,837
Let me start by saying I love this boiler. Everything about it is top shelf! Except for two minor, but important, details.
In order to perform a combustion analysis, you have to remove the flue gas sensor with a wrench in places an arm can barely reach, let alone a wrench and the wrench has a swing radius of about 3/16". On the KBN's, the flue sensor is on the outside of the boiler and just pulls out. Easy stuff. I get it done on the WHN's but it would be so much easier to have a capped port for it, ideally at the top of the boiler with a vent fitting that doesn't have to be glued (the second thing I'd like to see changed). Maybe something similar to what Buderus used (uses) on the GB142's?
I'll probably just go to the standard of drilling a 1/4" hole in the flue, tapping it, and plugging it when I'm done with a stainless steel tapered plug and a bead of high temp. silicone or the like on the threads.
Anyone else find this unnecessarily difficult or are my fingers just too fat?
Did I mention I love this boiler?
In order to perform a combustion analysis, you have to remove the flue gas sensor with a wrench in places an arm can barely reach, let alone a wrench and the wrench has a swing radius of about 3/16". On the KBN's, the flue sensor is on the outside of the boiler and just pulls out. Easy stuff. I get it done on the WHN's but it would be so much easier to have a capped port for it, ideally at the top of the boiler with a vent fitting that doesn't have to be glued (the second thing I'd like to see changed). Maybe something similar to what Buderus used (uses) on the GB142's?
I'll probably just go to the standard of drilling a 1/4" hole in the flue, tapping it, and plugging it when I'm done with a stainless steel tapered plug and a bead of high temp. silicone or the like on the threads.
Anyone else find this unnecessarily difficult or are my fingers just too fat?
Did I mention I love this boiler?
Steve Minnich
0
Comments
-
Max keeps a very short, metric open end to loosen that. It's plastic and usually comes out by hand once you get it loose.
If you were to vent with Centrotherm, they have a starter piece with a capped port. Sort of like the port on the TT.
Bob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream0 -
Thanks HR. Good to know. I'll have to get a shorty myself. I also picked up a length of 1/4" hose to bleed the vent up at the top of the boiler. I've been venting with CPVC this past year.Steve Minnich0
-
Help? On the left hand side is the flue gas sensor on the WHN. Would anyone happen to know what size metric wrench is need for the flats on the black plastic fitting?Steve Minnich0
-
looks like about a 12mm. Buy a whole set of double end, open ends metric wrenches at HD for 10 bucks or so. When you have the correct one, cut it down to about 4".Bob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream0 -
Thank you, Hot Rod.Steve Minnich0
-
I to am a fan of the WHN. love the control strategy. Especially the anti cycling feature for small loads. I couldn't agree more with the frustration of doing a combustion test. Every mod con out there has a port and some even on the combustion air side.
One other pet peeve ,minor, is I wish one of the heat demand contacts had priority so that if you have a small high temp load you could set it for priority and the pump/ ZV that is serving your low temp would shut down therefore saving the cost of a mixing station and increasing the efficiency of the overall system. I currently do the same thing with a switching relay but would be easier if it was built in to the controls.There was an error rendering this rich post.
0 -
Categories
- All Categories
- 86.5K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 423 Carbon Monoxide Awareness
- 94 Chimneys & Flues
- 2K Domestic Hot Water
- 5.5K Gas Heating
- 101 Geothermal
- 156 Indoor-Air Quality
- 3.5K Oil Heating
- 64 Pipe Deterioration
- 927 Plumbing
- 6.1K Radiant Heating
- 383 Solar
- 15.1K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 48 Job Opportunities
- 17 Recall Announcements