Tuning Indirect DHW Efficiency on TT Prestige Solo 110

Options
2»

Comments

  • hot_rod
    hot_rod Member Posts: 22,158
    Options
    If you lower them "A" side temperature to the heat exchanger, any heat exchanger, you lower then performance or output. That may or may not be acceptable for your needs. Recovery time will lengthen.
    No harm in dialing it down, it's adjustable so you have options.

    If you have any concerns with legionella bacteria growing in your tank, 140F is the recommended temperature to maintain in tanks.
    Bob "hot rod" Rohr
    trainer for Caleffi NA
    Living the hydronic dream
  • kolyan
    kolyan Member Posts: 17
    edited October 2020
    Options
    hot_rod said:
    If you lower them "A" side temperature to the heat exchanger, any heat exchanger, you lower then performance or output. That may or may not be acceptable for your needs. Recovery time will lengthen. No harm in dialing it down, it's adjustable so you have options. If you have any concerns with legionella bacteria growing in your tank, 140F is the recommended temperature to maintain in tanks.
    Well there is an option in setting for legionella. If that's enabled, it heats up tank to 140 once every week. So I am guessing thats enough to kill it

    Ps. As far as I understand maximum efficiency of the boiler is achieved when you lower the output to your desired needs. Pretty much same as heat modulation, its heating up the house with low water temps and you save money on gas because it doesn't have to heat it up all the way to 180+ when its not needed