Emerson filter driers & moisture indicators
NYplumber
Member Posts: 503
Hi wallies,
I have been particular to purchase Emersons EK lineup of filter driers and the HMI moisture indicators.
I was sold on the filter driers after watching a demonstration how they dont let filtered media past when the get vibrations from a compressor start up, etc.
The HMI sight glass moisture indicators supposedly show lower percentages of moisture then the competition.
Can anyone confirm the above statements before I go stock up? The local stores dont always seem to have these two products.
Happy HVAC'ing!
I have been particular to purchase Emersons EK lineup of filter driers and the HMI moisture indicators.
I was sold on the filter driers after watching a demonstration how they dont let filtered media past when the get vibrations from a compressor start up, etc.
The HMI sight glass moisture indicators supposedly show lower percentages of moisture then the competition.
Can anyone confirm the above statements before I go stock up? The local stores dont always seem to have these two products.
Happy HVAC'ing!
:NYplumber:
0
Comments
-
Happy HVACR'ing to you.
The Alco/Emerson SGMI,is slightly more sensitive than the Sporlan/Parker, but we are talking only just a little. 75-80 PPM vs around 100 PPM or so. Go w/ the SAE(flare) its easier to replace the FD and SGMI ,if needed.
I like both brands, but, IF/when there is a "comp burn out" w/ Acids, the acid breaks down the varnish on the comp motor windings and the varnish coats the yellow/green SGMI rendering it useless(depending) which means the SGMI should be replaced along w/ the comp. The yellow/green MI is a "salt derivative tablet" and the Alco SGMI is a "ceramic derivative tablet" and acid does not adhere to the ceramic tablet.
If there is ANY CHANCE of acid in the system use the "HH" version of the FD , the "HH" is for neutralizing Hydrochloric and Hydrofloric acids.
And it can take up to 24 hrs of running time for the SGMI to show its true color. I run across lots and lots of systems that need a 2nd and/or a 3rd FD change out. It is encouraged to go up a size or two w/ the FD. If there was an EK 163 (16 cu.in.)SAE FD you can go up to an EK-303(30 cu.in.)0 -
Thanks for the reply.:NYplumber:0
-
On a 2t AC I removed an 083 FD , put in a Sporlan C303-HH w/ SGMI and today I changed the FD a 2nd time, and w/ the MI showing a very, very light green mixed w/ a wonderful hint of yellow I think I might have to change the drier a 3rd time.
0
Categories
- All Categories
- 86K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 52 Biomass
- 421 Carbon Monoxide Awareness
- 81 Chimneys & Flues
- 1.9K Domestic Hot Water
- 5.3K Gas Heating
- 96 Geothermal
- 154 Indoor-Air Quality
- 3.3K Oil Heating
- 60 Pipe Deterioration
- 893 Plumbing
- 5.9K Radiant Heating
- 379 Solar
- 14.7K Strictly Steam
- 3.2K Thermostats and Controls
- 52 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements