Looking for photo of main vent on radiator riser

Options
I am helping out a single woman who is getting a new steam boiler. I noticed that there is no main venting on her one-pipe system. Part of her basement has finished ceilings, so it would be hard to find the end of the mains to tap for vents.

I recall seeing a post in the past of a main vent installed at the riser to a radiator. Does anyone know what the subject of the post is so I can share it with her contractor? Would installing a vent like this in a bedroom be a mistake, due to rushing air noise when the boiler cycle starts?

Thanks,

Steve Garson
Newton, MA
Steve from Denver, CO

Comments

  • nicholas bonham-carter
    nicholas bonham-carter Member Posts: 8,576
    Options
    If the main vent(s) are adequate in size, the air velocity should be very low, and quiet.
    What is the size, and length of the main leading to this end radiator? One Gorton 2 will handle 20 feet of 2 inch line.--NBC
  • Steamhead
    Steamhead Member Posts: 16,843
    Options
    Look at our Find a Contractor ad.
    All Steamed Up, Inc.
    Towson, MD, USA
    Steam, Vapor & Hot-Water Heating Specialists
    Oil & Gas Burner Service
    Consulting
  • Steve Garson_2
    Steve Garson_2 Member Posts: 712
    Options
    Thanks
    Steve from Denver, CO
  • Fred
    Fred Member Posts: 8,542
    Options
    Is this a single pipe sysem? That radiator would be the very first to get hot and probably would cause that room to be uncomfortable by the time the room with the Thermostat reached temp. Best thing to do is find a place at the end of the Main or somewhere along the return pipe in the basement for main vents. If it's a 2 pipe system, it may require a different approach, depending on the system type.
  • nicholas bonham-carter
    nicholas bonham-carter Member Posts: 8,576
    Options
    I think it will be alright, as this main vent would be at the end of the line. The main will fill, followed by all the rads, more quickly.--NBC
  • dennis53
    dennis53 Member Posts: 58
    Options
    There is a sketch on page 118 in TLAOSH along with a discussion of Frank Gerety and 'master venting' that may be what you are looking for. Similar on page 133 of Greening Steam.
    There is also a recent thread on venting risers.
    Good luck!
    http://forum.heatinghelp.com/discussion/152708/venting-mains-single-pipe-steam-system