Welcome! Here are the website rules, as well as some tips for using this forum.
Need to contact us? Visit https://heatinghelp.com/contact-us/.
Click here to Find a Contractor in your area.
Boiler Shutting Off / Cad Cell Relay Light Going On
Options
Jeff_H
Member Posts: 37
Recently, my Burnham V75 boiler has been shutting off and when I check to see why, I see the red light on the cad cell relay on. Fortunately, when I reset the cad cell relay, the boiler comes back on.
I have had the relay device swapped out (from a Honeywell to a GeniSys) and even had the motor changed, but I keep having the problem.
Could anyone recommend the next thing to look.
Thanks!
I have had the relay device swapped out (from a Honeywell to a GeniSys) and even had the motor changed, but I keep having the problem.
Could anyone recommend the next thing to look.
Thanks!
0
Comments
-
Ohms to high,Igniter trouble,oil delay valve, coupler slipping, pump screen, oil filter, plugged fuel line.... with a Genisys you can hook up a contractors tool and see why it is locking out on reset0
Categories
- All Categories
- 85.7K THE MAIN WALL
- 3K A-C, Heat Pumps & Refrigeration
- 51 Biomass
- 423 Carbon Monoxide Awareness
- 71 Chimneys & Flues
- 1.9K Domestic Hot Water
- 5.2K Gas Heating
- 92 Geothermal
- 149 Indoor-Air Quality
- 3.2K Oil Heating
- 60 Pipe Deterioration
- 850 Plumbing
- 5.8K Radiant Heating
- 375 Solar
- 14.5K Strictly Steam
- 3.2K Thermostats and Controls
- 51 Water Quality
- 38 Industry Classes
- 55 Job Opportunities
- 18 Recall Announcements