Warm Weather shut down ?
Danscrew
Member Posts: 130
I have a Weil Mclain WM97 Yesterday I happen to walk by the boiler and it was starting up and shutting down . So I popped the cover and started to investigate. I checked all the jacks going into the control board and everything was good. Next I started looking at the settings and I found the Warm weather shutdown set to 54 degrees and it was 53 OAT on the display. You would think it would have a Differential in the programming to stop it from banging on and off? So if the temperature stays at your set temp its going to bang on and off ? Not to good in the programming department . I raised it to 56 and it stayed on . Dan
0
Comments
-
Why not raise it up to 65 or so?0
-
Because I rather have the boiler shut down before my wife opens the windows with the T-stats on LOL after 54 or so the house don't need Heat I get plenty of son Dan0
-
that is sun LOL0
-
At 54*, I'd have to get plenty son....lol0