steam return piping lower than receiver inlet
Billy March_2
Member Posts: 57
I am piping out a steam coil on a unit that has the steam outlet piping too low for the condensate pump. The machine is on a concrete pad that is about 4 inches high and the steam return piping lands about 7 inches above finished floor.Condensate has to be pumped back to boiler room and the condensate pumps piping outlets are higher than the bottom of the steam coil. Digging the floor down and lowering the receiver to accommodate the needed piping height is NOT an option. Can I install a check valve on the piping after installing a steam trap and then jump up a few inches to make it to the inlet of the condensate pump or am I causing a problem with the steam trap being lower than the pump??
0
Comments
-
You'll have to run the steam pressure higher than normal to make that work, and if water collects in the coil while the pressure is down, returning steam would probably make it bang. Look for another solution that would let the condensate drain by gravity into the receiver, maybe you could pipe it into another part of the basement where the floor is lower.All Steamed Up, Inc.
Towson, MD, USA
Steam, Vapor & Hot-Water Heating Specialists
Oil & Gas Burner Service
Consulting0 -
As Steamhead said you can lift the condensate with steam pressure but not recommended unless there is no alternative.
The important thing is if the steam coil is heating outdoor air and a component fails, control valve, control, damper etc. you will freeze the coil for sure sooner or later if you are lifting the condensate0 -
Thanks for the replies. I will have to find an alternate solution...0
-
Probably can't raise the machine at this point??0
-
Find a condensate tank with two pumps. Take one pump out and fabricate a blank-off plate with a female thread acceptance. Or tap and thread the side of a one-pump tank. Might lose your warranty, though.0
-
Cut the slab, and lower the condensate tank?0
-
They make condensate tanks that are made to have the top flush with the floor Shipco Pump
.http://www.shipcopumps.com/products/index.php?category=condensate&id=type-duc0
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 916 Plumbing
- 6K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements