Expansion tank

BFlanzbaum
BFlanzbaum Member Posts: 26
I have review the wall for an answer and saw the Amtrol site. I need to replace a steel expansion tank but do not know the gallons in the system. The only info I have is the dimensions of the existing tank, so i can determine the gallons of the old tank but how do I select the bladder tank?

Thanks
«1

Comments

  • BFlanzbaum
    BFlanzbaum Member Posts: 26
    Thanks but I don't know system volume
  • wogpa67
    wogpa67 Member Posts: 238
    Is this for a house? If so use the residentil calculator. You'll need boiler net input and type of emitters.
  • BFlanzbaum
    BFlanzbaum Member Posts: 26
    Commercial building,Thank
  • Ironman
    Ironman Member Posts: 7,631

    Commercial building,Thank

    You'll need to estimate the system volume. There are online calculators that will tell you how much a given size pipe holds. That, plus the volume of your boiler and emitters will give you the amount to enter in the Amtrol calculator.
    Bob Boan
    You can choose to do what you want, but you cannot choose the consequences.
  • wogpa67
    wogpa67 Member Posts: 238
    As Iron said it's a little more involved.
    But too big is never a bad thing.
  • JUGHNE
    JUGHNE Member Posts: 11,318
    For what it is worth; the IBR manual has a "rule of thumb" for air cushion tanks (what you have now) of a volume of 1 gallon for each 5,000Btuh of total heat load.

    For bladder tanks they use 1 gallon of volume for each 7,000Btuh of total heat load.
    You could do the math to back engineer the existing tank to see what they might had used for a factor. And then use the calculated "heat load" with the bladder formula.
    Be aware that this is the residential guide, not commercial.
    Assuming that existing tank is large enough but is leaking??
  • BFlanzbaum
    BFlanzbaum Member Posts: 26
    So are you saying that even though I know that the existing tank is a 64 gallon tank, I cant convert that to something in a bladder tank ?
  • JUGHNE
    JUGHNE Member Posts: 11,318
    Is it leaking??
  • BFlanzbaum
    BFlanzbaum Member Posts: 26
    yes
  • JUGHNE
    JUGHNE Member Posts: 11,318
    It would seem that Amtrol would have a simple replacement chart somewhere. They want to sell tanks. Somewhere they have a replacement guide for well/pump tank cross reference and this seems like a similar situation. (Not the same application of course, but same problem). FWIW
  • JUGHNE
    JUGHNE Member Posts: 11,318
    edited March 2015
    Again FWIW; From Dan's book "How Come", page 31: Standard steel compression tank gallons X .55 if building is 2 stories tall or by .44 if 3 stories tall. Answer is volume of diaphragm tank.
    ( again be aware that this is residential??) Again bigger is better.

    That book also mentioned the "Vent-Rite" brand of tanks. Maybe check their site if they are still around.
  • hot_rod
    hot_rod Member Posts: 24,083
    edited March 2015
    Good info at the weasel site also, a better sizer program for non diaphragm type tanks

    Remember the difference air control or air management

    A plain steel compression type will be much larger, compared to a diaphragm or bladder style tank, as the air bubble is captive and maintained.
    Www.westank.com
    Bob "hot rod" Rohr
    trainer for Caleffi NA
    Living the hydronic dream
  • Jamie Hall
    Jamie Hall Member Posts: 25,376
    JUGHNE said:

    It would seem that Amtrol would have a simple replacement chart somewhere. They want to sell tanks. Somewhere they have a replacement guide for well/pump tank cross reference and this seems like a similar situation. (Not the same application of course, but same problem). FWIW

    Not the same application nor the same problem as a well/pump tank arrangement at all. The ONLY similarity is that one is using an air cushion for something.

    Frankly, if you don't understand that, it's unlikely that you will be able to understand how either an expansion tank (for hydronic) or a cycle control tank (for a well pump) works, and you certainly won't be able to size one correctly.

    Br. Jamie, osb
    Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England
  • JUGHNE
    JUGHNE Member Posts: 11,318
    edited March 2015
    Jamie, I understand very well how both type of tanks operate. My point was if they have a cross reference chart for water well tanks it seems there would be a cross reference from air cushion tanks to bladder.
    If the 64 gallon volume steel tank was large enough for the system then it should be a simple cross to bladder.
    And when replacing well water tanks in the past I would always go as large as space and money permitted for replacement.
    For that hydronic tank above I would go with the closest estimate and leave a tee in the piping to add 2nd tank if needed.
    Most likely ASME tank required so some money involved.

    Also; I am interested in this post as I may have the same replacement job in the near future.
  • Jamie Hall
    Jamie Hall Member Posts: 25,376
    There is a simple relationship for expansion control tanks for hydronic systems. Unfortunately, you do have to know the volume of water in the system, either the maximum operating temperature or the heat load, and also the operating pressure. Those variables don't seem to be known, at least for this thread; indeed, the OP specifically stated that he didn't know the water volume in the system.

    Well pump control tanks are sized on the basis of controlling the cycle time of the pump itself, and are related to the flow rate of the pump and the cutin and cutout pressures of the pump.
    Br. Jamie, osb
    Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England
    Harvey Ramer
  • JUGHNE
    JUGHNE Member Posts: 11,318
    Could we assume that the original designer/engineer knew the total volume of piping, radiation and boiler. Temp and pressure parameters etc. And then he, the designer, probably a long time ago, chose the 64 gallon air cushion tank. And we assume that it was sufficient for the system and the PRV didn't dribble or open. Then could we say the 64 gallon is correct, maybe even a little oversize? (safe engineering) ;)
    Then the question is what size bladder tank would do the same job that the original 64 gal air cushion tank did??

    As far as well tanks, there is a minimum size of course, but oversizing above minimum or using multiple tanks with matching air charges reduce pump cycling. Saving pressure switch, motor start components and rapid movement of the membrane(s) itself, prolonging tank life. That is another subject in its self.

    PS; sorry Jamie I hit the LOL on your post accidently :/
  • Jamie Hall
    Jamie Hall Member Posts: 25,376
    Absent any other information, sizing on the basis of the old 64 gallon tank would probably work just fine...

    And don't worry about the LOL!
    Br. Jamie, osb
    Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England
  • Harvey Ramer
    Harvey Ramer Member Posts: 2,261
    JUGHNE said:

    PS; sorry Jamie I hit the LOL on your post accidently :/

    Just click it again and it will go away.
  • JUGHNE
    JUGHNE Member Posts: 11,318
    Harvey, thanks for info, it is really good to have younger people around computers for us older folks. :) The LOL has left the wall.

    However the question still remains on what size of bladder tank equals the old 64 gal tank?
  • Harvey Ramer
    Harvey Ramer Member Posts: 2,261
    If the existing tank is properly sized, the answer is very simple. Start with a cold system and the exp tank drained. Reopen the fill valve and fire the boiler with all zones on. Once the boiler reaches high limit (180) close the valve to the compression tank. Drain the compression tank into 5 gallon buckets till empty. The gallons that you drained out will be the acceptance volume for the new bladder tank.
    kcoppZman
  • Jamie Hall
    Jamie Hall Member Posts: 25,376
    Clever, Harvey. I'll have to remember that. Thanks!
    Br. Jamie, osb
    Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England
  • Harvey Ramer
    Harvey Ramer Member Posts: 2,261

    If the existing tank is properly sized, the answer is very simple. Start with a cold system and the exp tank drained. Reopen the fill valve and fire the boiler with all zones on. Once the boiler reaches high limit (180) close the valve to the compression tank. Drain the compression tank into 5 gallon buckets till empty. The gallons that you drained out will be the acceptance volume for the new bladder tank.

    Actually there is one more step.
    You have to measure the initial fill water that enters the exp tank till it reaches system pressure, and subtract this amount from the amount that is extracted after the system reaches 180.

    The bladder tank will be precharged. Current tank isn't.
  • JUGHNE
    JUGHNE Member Posts: 11,318
    edited March 2015
    I really like a simple solution to such a conundrum. But I always have another question. As you open the tank fill valve before any hot water is produced, the tank will fill up about a third full. And then fire up to limit and more water should enter the tank?

    So the water added by thermal expansion plus the priming water for cold fill should equal the volume of a bladder tank?

    I don't know, I don't deal with that many exp tanks. As I mentioned one of these for change out might be in my future.
    But if your theory is correct you could have been hired by Thomas Edison. Part of his interview for engineers was to ask them to tell him the volume of a glass light bulb, not a simple shaped item. Those who measured and did a lot of complicated math were not hired. The ones who filled the bulb with water or sand (there are both versions) and dumped it into a measuring cup were deemed worthy of consideration for employment. I guess he was looking for common sense engineers.

    Edit: I always said I type to slow, referring to your "one more thing", (Colombo)
    PS Edit: you might still have a future with Edison. ;)
  • BFlanzbaum
    BFlanzbaum Member Posts: 26
    All interesting but the questions still remains.
  • Henry
    Henry Member Posts: 998
    In the old days when the bladder tanks first came out, a 30 gallon expansion tank was replaced by a EX30 and a 60 by a EX60. Depending on the input of the boilers and the operating temperaturre, you can either use an EX60 or a SX60. Amtrol does have literature to help you out. amtrol.com/media/documents/extrol/MC2680_01_15_EXTROL_Brochure.pdf
  • Paul48
    Paul48 Member Posts: 4,469
    I would have probably called tech support.
  • BFlanzbaum
    BFlanzbaum Member Posts: 26
    Just FYI if this changes anything for any of you . The input on the boiler is 1.2 mil
  • JUGHNE
    JUGHNE Member Posts: 11,318
    edited March 2015
    Is an ASME tank required for this application?

    Whenever I have a question like this in any of the trades I do, (electrical, HVAC & hydronics/steam), I run the problem by one of my Wholesale houses who has someone skilled in that trade.
    They have an interest in selling things, but not overselling/oversizing as they know you may ask 2 other houses for the same advice. And if they have any creditably they will sometimes eat their own mistakes.
    I always double check on my own as to their sizing advice, and ask them questions if something seems way out.

    They may also have a simple method to change the air handling/elimination if you go with a bladder tank.
  • BFlanzbaum
    BFlanzbaum Member Posts: 26
    I know the difference between bladder and diaphragm tanks physically, but when would you use each one.
  • JUGHNE
    JUGHNE Member Posts: 11,318
    I'm not familiar with which would be the best choice for your application. Hopefully someone on the wall here will help us both out.
  • SWEI
    SWEI Member Posts: 7,356
    Bladders can be replaced, which is a pretty big deal when you look at the cost of an ASME tank. Diaphragm tanks cost less (a LOT less if you don't need an ASME stamp) but are not repairable.
  • BFlanzbaum
    BFlanzbaum Member Posts: 26
    So no real function difference. When would you need as ASME tank
  • JUGHNE
    JUGHNE Member Posts: 11,318
    edited March 2015
    IMHO:
    Your leaking old tank may or may not be stamped ASME.

    But what probably matters today is:
    Does your local or city codes require it for commercial application?

    If the boiler is subject to annual insurance inspection, the company may insist on the ASME stamp.

    As you check price the differences you see it would be good to inquire.
  • icesailor
    icesailor Member Posts: 7,265
    Use this chart and folder. Page 5 of this PFD. It is rounded off to the BTU input of the boiler and the type of radiation.

    There may be other issues. But this one makes assumptions of size. A #60 or # 90 covers most all.

    http://www.amtrol.com/media/documents/extrol/MC2680_01_15_EXTROL_Brochure.pdf
  • icesailor
    icesailor Member Posts: 7,265

    Just FYI if this changes anything for any of you . The input on the boiler is 1.2 mil

    That would be found in a commercial rated tank. It would need a ASME rating. You probably need a floor mounted tank. What I posted is for a residential application.

    On another note, I don't believe that any water enters a pre-charged Extrol type tank until the pre-charge level is reached.

  • BFlanzbaum
    BFlanzbaum Member Posts: 26
    Great thanks for all your help
  • Don_197
    Don_197 Member Posts: 184
    edited March 2015
    In our area...............if any SINGLE appliance is rated at greater than 199,000 btuhs or has a greater than 119 gallon capacity, ASME is required. (now you know why there are 119 gallon 199,000btuh water heaters out there :D
    icesailorJUGHNE
  • EBEBRATT-Ed
    EBEBRATT-Ed Member Posts: 16,991
    In Mass. (and I think everywhere else) the State boiler inspectors require ASME expansion tanks if the relief valve on the boiler is above 30 psi. 30 and below non ASME tanks are ok, Above 30 ASME tanks. Hope this helps.
  • JUGHNE
    JUGHNE Member Posts: 11,318
    Don, that ASME requirement is the same in NE, I believe.

    But is the requirement for the appliance only? Not the expansion tank?

    I can see a lot of money in the investment.
    Again the OP needs to see what is required in his area.