True variable speed pump
Does anyone know of a true variable speed pump. One that can drop down to 1 or 2 GPM?
I have an HEC-2 and it doesn't slow down that much. The basic application is hot water baseboard circulator configuration, but not exactly.
thank you
  • Dave H_2
    Dave H_2 Member Posts: 622
    Joe,
    The HEC-2 does have a minimum speed (see here http://www.taco-hvac.com/uploads/FileLibrary/100-101.pdf) for the performance curve. You can get to the low speed and achieve that 1-2 gpm you are looking for. 1 to 2 gallons or minute is 20,0000 BTU's on a design day. If your system is about that size, you are right, it will be hard to vary below that speed.
    How much baseboard is connected to your system?
    Also, are you looking for a variable speed circulator or a high efficient ECM circulator?
    Dave H
    Dave Holdorf
    Taco, Inc
    Mad Dog_2
    EdTheHeaterMan Member Posts: 12,178
    Can you provide the total feet of element in your baseboard system. That is the part of your radiators with the aluminum fins. and how many fins per inch?
    And I believe @Dave H_2 may have a typo. The rule of thumb for 2 GPM is 20,000 BTU. (that is based on a 20° temperature drop between the supply temperature and the return temperature.)
    And you can get a Pump with temperature probe to be placed on the supply and return pipes and set the ∆T in order to get that 20° difference, or you can get a generic ECM that will just find a nice pressure differential without using the sensors.
    And Yes, you will get lower operating cost either way. So the question is do you only need lower cost operation, or do you want something else also?
  • Dave H_2
    @t4chi
    When this post was written in 2015, Taco had the option of AC variable speed circs and we also had a Delta T ecm at the time.
    These circs have a minimum speed and I was curious what we were connecting it to
    Dave Holdorf
    Taco, Inc
    hot_rod Member Posts: 27,452
    When you say "true variable speed" something needs to tell the circ what speed to run. Either sensors or the delta P operation, controlled by the algorithms in the software.
    If you want a manually adjustable ECM variable speed, the B&G Vario has a dial to dial in required speeds.
  • jumper
    jumper Member Posts: 2,538
    Varying the speed of any dynamic machine like a centrifugal pump cannot produce every flow one may want. You'd think that a positive displacement pump can……