PUMPING AWAY QUESTION
Tom Elam
Member Posts: 57
Greetings,
I have read the book Pumping Away and understand the concept and agree with it. I piped the boiler in my home that way with a Spirovent Jr and have no air issues anymore.
However in Caleffi's Idronics Tech Magazine Issue 2 page 23 of 36 they have a diagram that shows three possible locations for the Expansion Tank and Water Pressure Regulator. The air removal is on the hot water outlet of the boiler between the boiler and the suction side of the circulator. Their "ideal" location for the Expansion Tank and Water Pressure Regulator on the cold water return to the boiler. The "OK" location for the Expansion Tank and Water Pressure Regulator at the air removal device. The "never" location is on the discharge side of the circulator.
Has Caleffi got he "ideal and OK" locations backwards or has someone discovered a better way to remove air from the system?
I have read the book Pumping Away and understand the concept and agree with it. I piped the boiler in my home that way with a Spirovent Jr and have no air issues anymore.
However in Caleffi's Idronics Tech Magazine Issue 2 page 23 of 36 they have a diagram that shows three possible locations for the Expansion Tank and Water Pressure Regulator. The air removal is on the hot water outlet of the boiler between the boiler and the suction side of the circulator. Their "ideal" location for the Expansion Tank and Water Pressure Regulator on the cold water return to the boiler. The "OK" location for the Expansion Tank and Water Pressure Regulator at the air removal device. The "never" location is on the discharge side of the circulator.
Has Caleffi got he "ideal and OK" locations backwards or has someone discovered a better way to remove air from the system?
0
Comments
-
There doing it right it's all about you get more micro bubbles out when the heat is at its highest and the water flow is at its slowest.0
-
Thanks Snowmelt,
I am considering using a Spirovent VDR for my air and dirt removal. This will move the expansion tank and pressure regulator away from the air removal so I won't need a separate dirt trap.0
Categories
- All Categories
- 86.6K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 54 Biomass
- 423 Carbon Monoxide Awareness
- 97 Chimneys & Flues
- 2K Domestic Hot Water
- 5.5K Gas Heating
- 101 Geothermal
- 157 Indoor-Air Quality
- 3.5K Oil Heating
- 64 Pipe Deterioration
- 931 Plumbing
- 6.2K Radiant Heating
- 384 Solar
- 15.2K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 42 Industry Classes
- 48 Job Opportunities
- 17 Recall Announcements