Moline steam. Update to 2-pipe?

Timco
Timco Member Posts: 3,040
Between my friend and I we have seen about four Moline systems now.

Unless some knucklehead has removed the condensing loop or changed the return piping, is there any reason to update this to modern 2-pipe with a trap on each rad?

One of us says update. One of us says leave that thing alone.

Reasons?
Just a guy running some pipes.

Comments

  • Steamhead
    Steamhead Member Posts: 17,210
    Leave it alone. With a Vaporstat on the job this system will run nicely without the traps.
    All Steamed Up, Inc.
    Towson, MD, USA
    Steam, Vapor & Hot-Water Heating Specialists
    Oil & Gas Burner Service
    Consulting