trane condensing furnsce eating pressure switch

Paul_69
Member Posts: 251
in Gas Heating
10 yr old trane condensing furnace that keeps holding off pressure switches and we replace and runs for awhile.no water in switches and we flush condensate tubes etc. I believe there might be something wrong inside of one of the he.15%02 3.2co2 112 co 273 xair 2.3 wc for pressure switch. Maybe condensate trappoing in he causing pressure problems as it builds up? Seems to be better after we blow tubes out. I dont believe it is 7 switches faulty. calling tech support next week.
0
Comments
-
What are your o2 numbers before the blower fan motor come on?0
-
Is there any evidence of water in the top half of the furnace? I'm assuming it is an up flow furnace.0
-
Same o2 before blower on and during. Found out from trane the unit is 17 years old!!0
-
keep hose sag free may help.0