New CSST regs....
kcopp
Member Posts: 4,472
in Gas Heating
I got this from a Gastite Mfg. rep today.... interesting.
2015 model codes have been updated with respect to CSST bonding instruction.
The 2015 requirements allow the bond clamp to be attached anywhere on the fuel gas piping system (instead of upstream of the first section of CSST). This is helpful as this change can often result in shorter bonding wire lengths and/or simpler bond wire routings.
Additionally, the 2015 model codes limit the bond wire to a maximum length of 75 ft., and add that any additional grounding electrodes used shall be bonded to the grounding system.
The applicable section, 310.1.1 CSST, of 2015 IFGC is attached for your information.
2015 IFGC 310.1.1 Direct Bonding CSST
Gastite has updated its direct bonding requirements for Gastite CSST in technical bulletin TB 2014-01, posted at www.gastite.com . The direct link is below.
PDF Link: http://www.gastite.com/downloads/pdfs/Direct-bonding_TB2014-01.pdf
Gastite has also updated this info in the 2015 Gastite Design and Installation Guide, which will be distributed at the end of March.
2015 model codes have been updated with respect to CSST bonding instruction.
The 2015 requirements allow the bond clamp to be attached anywhere on the fuel gas piping system (instead of upstream of the first section of CSST). This is helpful as this change can often result in shorter bonding wire lengths and/or simpler bond wire routings.
Additionally, the 2015 model codes limit the bond wire to a maximum length of 75 ft., and add that any additional grounding electrodes used shall be bonded to the grounding system.
The applicable section, 310.1.1 CSST, of 2015 IFGC is attached for your information.
2015 IFGC 310.1.1 Direct Bonding CSST
Gastite has updated its direct bonding requirements for Gastite CSST in technical bulletin TB 2014-01, posted at www.gastite.com . The direct link is below.
PDF Link: http://www.gastite.com/downloads/pdfs/Direct-bonding_TB2014-01.pdf
Gastite has also updated this info in the 2015 Gastite Design and Installation Guide, which will be distributed at the end of March.
0
Comments
-
Things were sweet for a few years with the strike diffusion jackets, but lately I've had inspectors tell me they need bonding with that too. Meant to ask a few vendors out at Chicago what's up with that and heck, why not just go back to the yellow stuff?0
-
I'll just continue to cut and thread pipe myself. Don't trust that stuff for gas.
Most of the boilers I Install are a split. Half press and half I'll cut and thread.
0 -
Here in NH you still need to bond no matter what. I still most of the time cut and thread. The only time I use csst is if it would be very difficult to do blk steel.0
-
If I followed that correctly, they are referring to the yellow gastite. Flashshield (black) is not mentioned in the bonding requirements.
0 -
Same here in Pa. Easy to bond black pipe..0
-
In December, 2014, Massachusetts the 2012 National Fuel Gas Code (NFPA 54) with State Amendments. There's always been a lot of misinformation on how CSST can be used. The Trade Show issue of NE Progress/PHCC has a good rundown. Its worth the read. Whether you use it, like it, or hate it, its not going away. Each and every kind is "System" and not a component. With the changes, people will need to be recertified for the different "Systems".0
-
Black jacket or yellow... I am required to bond. I do run into a lot of systems that were installed prior to all the bonding requirements. I am required to bond them if I see them.0
-
Me, i just don’t like it,but not to say anything wrong with it…I saw some at the big box store….Maybe some people use it for water…..LOL0
-
Yeah, I noticed this code change a couple weeks in my gas update class. They also said we can use press fittings and copper pipe on LP if the fuel provider is ok with it.Tom
Montpelier Vt0 -
I don't see how they can sell it at a big box store. Under NFPA 54, it is considered a "System" and not a "Component". Part of their approval process long ago was that you had to be trained and certified to use it by each and every manufacturer to install their "System". If you are not certified to install it, how can you install it, I have 5 certification cards in my wallet. Some go back as far as the 1990's. TracPipe and Wardflex CSST tubing aren't compatable with each others tubing. The spacing is different.j a said:Me, i just don’t like it,but not to say anything wrong with it…I saw some at the big box store….Maybe some people use it for water…..LOL
If Johnny "DIY Homeowner goes to HD, and buys a bunch to re-gas pipe his house, does the auto-check out scan his certification? The women in the regular check out line?
If the CSST manufacturers are so hungry to sell their products to the public at big box stores, maybe the product should be removed from approval. While I was active, any time I went in a strange store where they didn't know me, they asked me for my certification card. They're not supposed to sell the product to uncertified installers. If I am certified for Wardflex and not Track Pipe, and I go to purchase TrackPipe, they're not supposed to sell it to me.
0 -
Totally agree. Its a train wreck happening and there is not a thing we can do about it...very sad...hopefully the new younger guys get a handle on this. I think most homeowners and the unlicensed understand...its not that they are by any means unskilled and not capable...so clearly no ofence to them....I Mass at least it the law....thank God...
.0 -
Did they ever test ANY of this stuff in a lightning lab? That was the big sticking point in law suits from a few years back. The manufacturers couldn't even show that it had been tested in a lightning lab. I se one good resolution to the use of this stuff, previous and future.
Require a solenoid shut off valve connected to the fuel supply outside of the building that is controlled by a "near lightning strike detector", that if lightning is detected, it shuts the fuel system down and requires a technician to come out and test for vessel integrity. Once integrity is confirmed, controller is reset and fuel restored.
We have the technology...
I had a 3.5 million dollar house burn to the ground, allegedly due to this material, and a lightning strike that hit 6/10 of a mile away.
As I told their lawyer during deposition, who asked me if I would EVER consider using their product in the future (and I didn't install the stuff in the house that burned to the ground, was there consulting on other heating "issues")
I responded "Sure... Show me some place on the face of this big blue marble that has a high Earthquake potential, and no lightning, and I will use it till the cows come home..." He didn't like my answer.
NIMBY, or my customers homes.
METhere was an error rendering this rich post.
0 -
@icesailor
Around here, in Connecticut, they sell CSST and fittings at HD... it does however have a sticker on it saying something along the lines, "only to be installed/purchased by licensed....". If I remember correctly. They definitely sell gas fittings (ball valves, IPS) to anyone.
I found it interesting that they had it... however I don't know if there are any stipulations to buying it. As in does HD enforce sales to only licensed professionals. I know there aren't home inspections/permits needed in every part of the US... so why would they (home centers, supply houses, etc…) require licensed professionals to purchase the product.
Hell, you can buy black pipe and they won't know if your using it for gas or not. I think it’ll come down to your local jurisdiction and whether they require permits and/or a licensed professional to install. I don’t know about gas… but I’ve down everything else in the house, with permits and the inspector signs them off when he’s satisfied.0 -
-
Sometimes even the pros screw up guys . Right here in my area , look at what the gas company did . This is bad but really cool lookin , will make people think about gas DIY .
https://video.search.yahoo.com/yhs/search;_ylt=A0LEVvcCqvhU814AvA8lnIlQ;_ylu=X3oDMTB0ZjNuMHJ1BHNlYwNzYwRjb2xvA2JmMQR2dGlkA1lIUzAwM18x?p=Stafford+township+gas+explosion&hspart=mozilla&hsimp=yhs-004
Oh yeah , a second one that week .
http://www.thestate.com/2015/03/02/4020077/man-hurt-in-2nd-recent-gas-explosion.htmlYou didn't get what you didn't pay for and it will never be what you thought it would .
Langans Plumbing & Heating LLC
732-751-1560
Serving most of New Jersey, Eastern Pa .
Consultation, Design & Installation anywhere
Rich McGrath 732-581-38330 -
I agree with ME. We won't use it, for the same reason. For us, black threaded steel or someone else can have the job and the liability.All Steamed Up, Inc.
Towson, MD, USA
Steam, Vapor & Hot-Water Heating Specialists
Oil & Gas Burner Service
Consulting0
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 917 Plumbing
- 6.1K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements