slow closing valve
billygoat22
Member Posts: 124
I have a customer that system has developed slamming noise/ waterhammer. when more than one zone is calling and one closes, gets a banging.
if I slow the rate of closing on zone valves by easing on shut, (honeywell 8043) do not get slamming. If one zone running, no noise when closes, since pump shuts off as it closes.
waould like to know if I can retrofit a slow closing valve motor in place of the existing motor to stop the waterhammer? thanks.
if I slow the rate of closing on zone valves by easing on shut, (honeywell 8043) do not get slamming. If one zone running, no noise when closes, since pump shuts off as it closes.
waould like to know if I can retrofit a slow closing valve motor in place of the existing motor to stop the waterhammer? thanks.
0
Comments
-
Zone valve backwards?0
-
Often that hammer is caused by too much pump. Or the valve is in backwards
If it's possible. Delta P circ is a nice fix, and it reduces power consumptionBob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream0 -
valves in right, 1st thing I checked. only one pump for system. has 4- 3/4" lines, one of which is domestic hot water. other three are series loop basebd circuits for each floor.0
-
Simple fix. Remove the cover on the zone valve and you will see two springs. Unhook one end of the spring that is easily assessable with fine needle nose pliers. This will allow the valve to close slowly.0
-
If it just "developed", what changed? Was it always there?
What type of circulator is installed?
More often than not, it could be just the application and choosing the correct circ for the project. Variable speed circs can and will help, but without knowing what changed, you just dont want to throw money at it and hope that is fixes it.
I always want to know exactly whats wrong/changed/ so that it fixes it the first time.
DaveDave Holdorf
Technical Training Manager - East
Taco Comfort Solutions
0
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 916 Plumbing
- 6K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements