brass or dielectric unions for stainless indirect to copper boiler piping
thoughtfulTom
Member Posts: 18
We used to use Munchkin's, and their stainless water heaters. As I recall, they insisted we not use di-electric unions on the boiler connections.
Now we have switched to Lochinvar, and their stainless steel water heaters. The manufacturer's rep say they don't care between brass and di-electric unions. I would like to utilize best practice here, but I don't know which is better between the two. The fittings are stainless mail nipples at the water heater indirect loop, going to the copper piping to/from the boiler.
What is the best way to proceed?
Now we have switched to Lochinvar, and their stainless steel water heaters. The manufacturer's rep say they don't care between brass and di-electric unions. I would like to utilize best practice here, but I don't know which is better between the two. The fittings are stainless mail nipples at the water heater indirect loop, going to the copper piping to/from the boiler.
What is the best way to proceed?
0
Comments
-
-
304 or better 316 are in the cathodic range and with copper the potential between the two is small, even in a constant electrolyte. Brass will be the anode especially yellow brass with stainless. The lower the zinc content in the brass alloy the less problems possible. Will really depend on your water TDS and gases to know how aggressive the galvanic corrosion will be in this scenario. if lockhnivar isn't concerned then I would not worry. Dielectric unions be more of a headache down the road than the actual corrosion you are trying to stop.1
-
This is on the boiler side, not the DHW side, correct?0
-
Someone stole my digital camera with all my digital photos of leaking dialectic unions on LPG services from underground tanks. WHile I was walking around a house I was turning the water in in the spring, I would catch a whiff of Mercaptan and my nose would lead me right to the regulator. The unions were always AFTER the tank and before the regulators so I could shut them off.0
-
SWEI - this is on the To/from boiler connections for the heat exchanger coil inside the water heater, the connections are at the water heater - male stainless stub-outs.0
-
As long as you keep the system airtight, pretty much anything will work.
On the domestic side, as pointed out above, stainless and copper are fine together. Dielectric unions fail. A lot. We avoid them like the plague. If there is a genuine need for dielectric isolation, a foot or two of PEX or Aquatherm will do the job far better.2 -
We also avoid dielectric unions.
Unless you want to make service calls for the future. Easy to diagnose. Just walk in and point to the dielectric union.Al Corelli0 -
Try explaining that to the ME.SWEI said:As long as you keep the system airtight, pretty much anything will work.
On the domestic side, as pointed out above, stainless and copper are fine together. Dielectric unions fail. A lot. We avoid them like the plague. If there is a genuine need for dielectric isolation, a foot or two of PEX or Aquatherm will do the job far better.0 -
Die electric unions do just that , they die.
Unless a requirement go with dezincified brass or copper.0 -
That's because they're smart and overeducated. We're not.RobG said:
Try explaining that to the ME.SWEI said:As long as you keep the system airtight, pretty much anything will work.
On the domestic side, as pointed out above, stainless and copper are fine together. Dielectric unions fail. A lot. We avoid them like the plague. If there is a genuine need for dielectric isolation, a foot or two of PEX or Aquatherm will do the job far better.
0
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 916 Plumbing
- 6K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements