Transformer and relay
Boston_2
Member Posts: 107
in Gas Heating
This may be a silly question, but could someone explain to me why is there a need for both a transformer and relay in my boiler? Is it for the gas valve? We had an outdoor reset installed and now once in awhile i get some chatter from the relay? Is it possible the end switch on the reset is causing the relay to hum/chatter?
0
Comments
-
The transformer steps the 110 volt line voltage down to 24 volts to run the thermostat circuit. The relay pulls in when the thermostat calls for heat, and activates the burner(24volts) and the circulator(110volts) at the same time, without mixing the two voltages. If your relay is chattering, you probably have a problem with the 24 volt side.0
-
Chattering usually means time to replace. But first check that the leads to the relay have not come loose.0
-
Is it a Burnham?0
-
Yes, it's an older Burnham. I'm still checking the othe suggestions about about voltage.0
-
This content has been removed.
-
I don't see a pic...but take off the front cover and there is a relay in there wiggle it around. Famous for the chattering..on Burnham. Loose connection or something..when we install them. We put a tiewrap around it.....saves a call back or 2.... If bad its a common and cheap part....I am only guessing because I am not there and don't see a pic0
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 64 Pipe Deterioration
- 919 Plumbing
- 6.1K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements