About Vaporstat install
RobLC
Member Posts: 93
Currently, we have a P404A Honeywell Pressuretrol. This units differential settings are 1 to 5 lbs. It is single phase, has one black wire and one red wire coming from the on/off switch for the boiler. The boiler is an old gas-fired steam boiler.
The current settings are .5 for the cut-in and almost 1.5 (more like 1.3) for the differential.
We would like to install a Vaporstat.
What would be the best model and settings, e.g., Honeywell model ? and cut-in ounces and differential, cut out?
Thank you.
The current settings are .5 for the cut-in and almost 1.5 (more like 1.3) for the differential.
We would like to install a Vaporstat.
What would be the best model and settings, e.g., Honeywell model ? and cut-in ounces and differential, cut out?
Thank you.
0
Comments
-
L408J1009
settings vary depending on your situation, but I like to start at about 12 oz with a 8 diff0 -
Ok, thank you for the info. Then we'll try 12oz and 8oz. This would mean that Vaporstats are subtractive?
0 -
yes.. the 2nd setting is a subtractive differential. So 12oz with 8oz diff setting means off at 12oz and on at 4oz0
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 916 Plumbing
- 6K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements