Wi-Fi thermostat with tekmar (260)? Has anyone done it?
Options
JohnNY
Member Posts: 3,230
Hello all,
I need to control a system pump and boiler pump with a cast iron boiler. That's a 260 to me.
Client wants a wi-fi thermostat (Red Link?) to work with his iPhone.
I've never coupled these two pieces before.
I assume I'll need a relay between the stat and the heat demand on the tekmar. Seems convoluted to you too?
Any help is appreciated.
I need to control a system pump and boiler pump with a cast iron boiler. That's a 260 to me.
Client wants a wi-fi thermostat (Red Link?) to work with his iPhone.
I've never coupled these two pieces before.
I assume I'll need a relay between the stat and the heat demand on the tekmar. Seems convoluted to you too?
Any help is appreciated.
Contact John "JohnNY" Cataneo, NYC Master Plumber, Lic 1784
Consulting & Troubleshooting
Heating in NYC or NJ.
Classes
Consulting & Troubleshooting
Heating in NYC or NJ.
Classes
0
Comments
-
-
Thank you, Joe.
I was inclined to follow a schematic like this one without the relay, but I do like having options.Contact John "JohnNY" Cataneo, NYC Master Plumber, Lic 1784
Consulting & Troubleshooting
Heating in NYC or NJ.
Classes1 -
I thought that the Boiler Demand sent power out and should not have voltage applied to it....?0
-
As long as the stat can close a relay, shouldn't need isolation. If for some reason the stat has a TRIAC instead of a relay, it gets a little more complex.0
-
Boiler demand requires power in. 20-280v.
Can be make or break via a thermostat or other switch, but I often like to set it up with a constant demand and let it work off WWSD.
Every job is different....Contact John "JohnNY" Cataneo, NYC Master Plumber, Lic 1784
Consulting & Troubleshooting
Heating in NYC or NJ.
Classes0 -
Gotcha. 24 VAC from pretty much anyplace you can find it will work since it's essentially zero load.0
Categories
- All Categories
- 85.6K THE MAIN WALL
- 3K A-C, Heat Pumps & Refrigeration
- 51 Biomass
- 423 Carbon Monoxide Awareness
- 71 Chimneys & Flues
- 1.9K Domestic Hot Water
- 5.2K Gas Heating
- 92 Geothermal
- 149 Indoor-Air Quality
- 3.2K Oil Heating
- 60 Pipe Deterioration
- 850 Plumbing
- 5.8K Radiant Heating
- 375 Solar
- 14.5K Strictly Steam
- 3.2K Thermostats and Controls
- 51 Water Quality
- 38 Industry Classes
- 55 Job Opportunities
- 18 Recall Announcements