Hello all,
I need to control a system pump and boiler pump with a cast iron boiler. That's a 260 to me.
Client wants a wi-fi thermostat (Red Link?) to work with his iPhone.

I've never coupled these two pieces before.
I assume I'll need a relay between the stat and the heat demand on the tekmar. Seems convoluted to you too?
Any help is appreciated.
Contact John "JohnNY" Cataneo, NYC Master Plumber, Lic 1784
Consulting & Troubleshooting
Heating in NYC or NJ.
Classes

Comments

  • JStar
    JStar Member Posts: 2,752
    Options
    Honeywell R8845U. We use this relay to interface all of our wifi tstats. It has a dedicated Common terminal, a control fuse, and three sets of dry contacts.
    Tinman
  • JohnNY
    JohnNY Member Posts: 3,230
    Options
    Thank you, Joe.
    I was inclined to follow a schematic like this one without the relay, but I do like having options.
    Contact John "JohnNY" Cataneo, NYC Master Plumber, Lic 1784
    Consulting & Troubleshooting
    Heating in NYC or NJ.
    Classes
    Tinman
  • SWEI
    SWEI Member Posts: 7,356
    Options
    JohnNY said:

    I assume I'll need a relay between the stat and the heat demand on the Tekmar.

    No need for a relay there.
  • JStar
    JStar Member Posts: 2,752
    Options
    I thought that the Boiler Demand sent power out and should not have voltage applied to it....?
  • SWEI
    SWEI Member Posts: 7,356
    Options
    As long as the stat can close a relay, shouldn't need isolation. If for some reason the stat has a TRIAC instead of a relay, it gets a little more complex.
  • JohnNY
    JohnNY Member Posts: 3,230
    Options
    Boiler demand requires power in. 20-280v.
    Can be make or break via a thermostat or other switch, but I often like to set it up with a constant demand and let it work off WWSD.
    Every job is different....
    Contact John "JohnNY" Cataneo, NYC Master Plumber, Lic 1784
    Consulting & Troubleshooting
    Heating in NYC or NJ.
    Classes
  • SWEI
    SWEI Member Posts: 7,356
    Options
    Gotcha. 24 VAC from pretty much anyplace you can find it will work since it's essentially zero load.