Steam boiler losing water
Do any of the boiler return pipes go under the cellar floor, any steam feeds or returns in crawl spaces? Look at the chimney when the boiler is making steam and see if it seems to be putting out a larger plume than you neighbors does.
3PSI gauge0 -
Try overfilling the boiler up to the header. let it cool down first, and leave it off while overfilled. Look inside the firebox, and around the base for any signs of a leak.
Can you see the wet returns close to the floor in the basement? The increased pressure of the overfilled boiler should show any existing leaks in the returns as well.
when you have looked at everything carefully, then drain the waterline back to its normal operating height, and turn it back on.--NBC0 -
How old is the boiler? Do you notice any wet spots on the basement ceilings? any radiator vents/valves/joints/fittings leaking? Does the boiler build any pressure when it runs for an extended period(even a couple ounces)?
How much water do you have to add daily?
As far as the water hammer is concerned, if you can identify the area where the hammer occurs, look for a Main or radiator supply pipe that may be level or pitched the wrong direction or that may have a sag in the pipe. Radiator runs should pitch back towards the Main and the Main should pitch towards the return end, heading back to the boiler. Also, check that the radiators, in the area of Hammer, and make sure the radiator is pitched back towards the steam valve/pipe. You can use shims under the Vent end of the radiator to get pitch.0 -
Boiler is 3 years old
No wet spots in the basement
previously had one supply valve that leaked but replaced that and no leaking anymore.
Boiler builds pressure and cuts out at 2 psi through the pressuretrol. no lack of steam pressure.
i add water about every 3-4 days.about 1.5" through the siteglass of water
All radiators are pitched back towards the supply valve via a shim
i checked this last night and there is no large amount of steam coming from the chimney when its firing. i dont see anything coming out of the chimney at all.BobC said:Do any of the boiler return pipes go under the cellar floor, any steam feeds or returns in crawl spaces? Look at the chimney when the boiler is making steam and see if it seems to be putting out a larger plume than you neighbors does.
Bob
Return pipes all run above grade below the first floor until it gets to the boiler and is still above the floor and back into the boiler.
The one thing i did notice is that on the manual water feed valve to the boiler. whenever the boiler is on and firing the valve itself drips. from the stem thats about it.0
You have a vent, valve or fitting somewere on the system that leaks. They can be hard to find because the the boiler is running, the water steams away and it is almot impossible to see. Take our time and inspect every fitting and valve/vent. Look for any signs of moisture rusty drips.
The obvious next question is can you post oe picures of the system, boiler and mains/returns?0 -
I inspected the supply valves on the other radiators which are the original ones from 1950 or so, and noticed alot of dried rusty drips. but when the boiler is running i dont see any moisture at all. is it recommended that i change them all out?Fred said:You have a vent, valve or fitting somewere on the system that leaks. They can be hard to find because the the boiler is running, the water steams away and it is almot impossible to see. Take our time and inspect every fitting and valve/vent. Look for any signs of moisture rusty drips.
there are two radiators on the second floor that i noticed spit a little bit of water - like a drop or so, but not enough to be losing that much at the boiler.
There's no reason to change out those valves. Sometimes water steams away from a joint/pipe and it's not noticable. I had a flange joint that steamed so subtly, in the basement that it took me most of a heating system to finally find it. When water leaves the system, it is going somewhwere. just keep an eye on things.0
Being oversized is more common than most of us want to believe. It can cause short cycling depending on how long the boiler runs but won't cause water loss.
Unrelated to your losing water, but header should be at least 2.5". Looks like they reduced the riser to 2" and ran 2" header.0
Weil Mclain actually says in the manual that it can be reduced down to 2". I don't agree with it, but that's what it says.Abracadabra said:Unrelated to your losing water, but header should be at least 2.5". Looks like they reduced the riser to 2" and ran 2" header.
1
- 167 Indoor-Air Quality
