how do i temper hot water "cooler" and chilled water "warmer" with one 4way valve & controller
pipeking
Member Posts: 252
a lot has change since I've last been on the wall, sorry....
so I have 2 temp heating (hydro air, radiant) which I have know problem with, but this my first 2 temp cooling. so the chilled water for my air handlers will be to cold for my radiant, can I use one 4 way valve to do my heat and cooling tempering with a 2 stage controller? what have you done in this situation? what brand have u used? simplicity is king!
so I have 2 temp heating (hydro air, radiant) which I have know problem with, but this my first 2 temp cooling. so the chilled water for my air handlers will be to cold for my radiant, can I use one 4 way valve to do my heat and cooling tempering with a 2 stage controller? what have you done in this situation? what brand have u used? simplicity is king!
0
Comments
-
Do you plan on running these simultaneously ?You didn't get what you didn't pay for and it will never be what you thought it would .
Langans Plumbing & Heating LLC
732-751-1560
Serving most of New Jersey, Eastern Pa .
Consultation, Design & Installation anywhere
Rich McGrath 732-581-38330 -
yes. heating radiant and heating hydro. cooling radiant and cooling/dehumidify hydro. aaand heating radiant with cooling/dehumidifying hydro.
a little complex, but its pretty much all coverd, except, I don't know who makes (or even exsists) a floating 4 way valve, with a controller that will do this0 -
What is / are source / s for this application ?You didn't get what you didn't pay for and it will never be what you thought it would .
Langans Plumbing & Heating LLC
732-751-1560
Serving most of New Jersey, Eastern Pa .
Consultation, Design & Installation anywhere
Rich McGrath 732-581-38330 -
Belimo would be a good place to look.Bob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream0 -
modine geofinity ground source heat pump, and an HTP elite. Should that matter?0
-
The belimo might not work, the valve I'm looking for will have the 9 zones of radiant on it (the whole house). That particular valve comes in 3/4". what would I used to control that?0
-
This is a home obviously so may I ask why A/c and heating would be running simultaneously ?
Hot Rod , I know you have a nice radiant heating and cooling control picture in one of those I Dronics issues , cannot remember which one .
You didn't get what you didn't pay for and it will never be what you thought it would .
Langans Plumbing & Heating LLC
732-751-1560
Serving most of New Jersey, Eastern Pa .
Consultation, Design & Installation anywhere
Rich McGrath 732-581-38330 -
It's would be heating and dehumifcation. It's is a "super efficient" home, sealed tight and the homeowner/very successful architect is worried about humidity. There is an erv. for fresh air recurculation. So this is where I'm at....0
-
Rich said:
This is a home obviously so may I ask why A/c and heating would be running simultaneously ?
Hot Rod , I know you have a nice radiant heating and cooling control picture in one of those I Dronics issues , cannot remember which one .
Good memory, Rich
May be some helpful info here
http://www.caleffi.com/sites/default/files/coll_attach_file/idronics_13_0.pdfBob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream0 -
The six way valve is intended for terminal applications in a four pipe system (typically found in commercial buildings having glass curtain walls.) They are designed for flow rates under about 6 GPM.
What exactly are you trying to accomplish? A pair of 3-ways (which Belimo makes in sizes for flows of <1 GPM through ~200 GPM) can do pretty much the same thing with proper wiring and switching.0 -
pipeking said:
The belimo might not work, the valve I'm looking for will have the 9 zones of radiant on it (the whole house). That particular valve comes in 3/4". what would I used to control that?
Maybe not that valve specifically but Belimo makes thousands of special purpose valves most available with a choice of actuators. just an idea for a place to shop.Bob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream0 -
i guess its not so much the valve and actuator im having a problem with, its controlling it.0
-
Can you describe what you're trying to do? I might have some ideas.0
-
I have a hot water buffer and and a cold water buffer, between the 2 tanks I should have good sequence of operation with 3way diverting valves, pumps and checks. They will supply a header for my air handlers and a Header for my radiant. The air handler header comes first and will get tank temp. The radiant is second and will have tempered water. I need a control that will meter my mixing valve for 160*to85*f+/-, and from 38*to60*+/-. This controller will prolly have supply temp sensor and know when to switch Temps, or even better have an unlimited temp. reset.0
-
what controller will do this0
-
Sounds like you are describing a two pipe system -- hot water in winter and cold water in summer, all running through the same pipes, valves, tanks, and emitters?0
-
so I went with tekmar mixing setpoint control 153, and im going to have to install 2. one for chilled temps and one for heat temps, and switch between the 2 with sequencing. thanks anyway0
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 917 Plumbing
- 6.1K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements