F&T trap install
Johncapn
Member Posts: 21
I have been diagnosing and improving our two pipe steam system in a 9,000 sq ft nixed use Building in Boston that I own and renovated. It appears that several "Steam experts" in our area let us down on this. The last one in suggested we replace the Barnes and Jones F&T traps for these Mepco traps.
I have had issues getting steam to the furthest radiators in the system on one leg of the steam main and it appears that the install of these traps may be a problem. To my mind the condensate and air that is supposed to exit these traps has to run Uphill.
One symptom I am having is bouncing pressure gage at the boiler. I have a 2 year old Boiler which was drained down in the fall so I don't think it needs skimming as the sight glass only shows rusty water. With help from the forum so far I diagnosed missing cage units in steam traps and remedied that. I have managed to reduce running pressure from 3PSI to 12oz.
Any thoughts?
I have had issues getting steam to the furthest radiators in the system on one leg of the steam main and it appears that the install of these traps may be a problem. To my mind the condensate and air that is supposed to exit these traps has to run Uphill.
One symptom I am having is bouncing pressure gage at the boiler. I have a 2 year old Boiler which was drained down in the fall so I don't think it needs skimming as the sight glass only shows rusty water. With help from the forum so far I diagnosed missing cage units in steam traps and remedied that. I have managed to reduce running pressure from 3PSI to 12oz.
Any thoughts?
0
Comments
-
-
-
-
Thanks Fred and Abracadabra. There is some "bounce" in the sight glass when the boiler is running would that show up in the pressure gage as the needle bouncing around?0
-
JStar, our system uses crossover traps around the steam mains and I am venting at the end of the dry returns. However as the steam gets to the end of the Steam Mains the crossover traps become fewer. Perhaps a couple of Gorton #2's would help? However the F&T traps are in a clothing store and a shoe repair store. Will they drip water or hiss loudly?JStar said:You should install a main vent on the unused top plug of that F&T trap, and keep it raised above the height of the main.
0 -
What size and length of pipe between the last cross-over trap and the F&T trap?0
-
If I have time today (still shoveling in Boston) I will try a Boiler skim.
Thanks for the help so far...0 -
Jstar, about 3 feet in length. Bout half of it is the steam main and half is 2' pipe. the crossover can be seen in this photo teeing off the steam main in the top right of the shot.JStar said:What size and length of pipe between the last cross-over trap and the F&T trap?
0
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 64 Pipe Deterioration
- 917 Plumbing
- 6.1K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements