3/8" PEX for panel home run system
There are a lot more options in 1/2", however my biggest radiator has a load ~ 7000 BTUs. Given a delta T of 20-30* my flow rates in 3/8" are reasonable, while maintaining close to 2FPS. With 1/2" I think I would be over-pumping to maintain at least 2FPS.
Locally I know for sure I can get ROTH and Uponor tubing.
Comments
-
Larger dia. tubing has little consequence other than workability, and cost. Another thought is your radiant floor. sandwich or underfloor?
running in the 4-5 FPS range is not a problem.0 -
Yum sorry to say or ask I'm confused by the question, are you asking what pex brand I use?0
-
3/8" PEX-a routed through the walls. Transition to 1/2" copper if routed through the floors.0
-
I would use 1/2" for the fact that it's a more common size and fittings are readily available.0
-
Ditto bob0
-
Radiant floor in bathroom will be dry sandwich. Future addition will be in slab.Gordy said:Larger dia. tubing has little consequence other than workability, and cost. Another thought is your radiant floor. sandwich or underfloor?
running in the 4-5 FPS range is not a problem.0 -
Sure, what do you guys like to use for sizing and brand/type. There are a lot of options from different manufacturers, PEX-a, PEX-b, PEX-c, PE-RT, PEX-AL-PEX, PERT-AL-PERT....Snowmelt said:Yum sorry to say or ask I'm confused by the question, are you asking what pex brand I use?
0 -
They'll be routed in/under floor joists (basement), then thru floor to panels (Buderus, bottom connection).SWEI said:3/8" PEX-a routed through the walls. Transition to 1/2" copper if routed through the floors.
0 -
With 1/2" tubing, my rough calculations indicate that to keep flow velocities at 2+ FPS the required GPM would result in delta Ts ~12* (design day) and would only get smaller as temps go up.
Maybe doesn't really matter... 1/2" is a lot easier to find fittings for.0 -
Big fan of Viega Fostapex. Readily available fittings, tools don't cost an arm and a leg. When Uponor (then Wirsbo) came out with MultiCor, 15 years or so ago, I was pumped (pun intended) but back then fittings were limited, and the crimp system was very new. And obscenely expensive. Looked at Kitec briefly but they vaporized. Then Fostapex came to market. Sold.0
-
-
The bottom connections work great with either 1/2" or 3/8" PEX. No worries about sagging like the top end pipe does.bmwpowere36m3 said:They'll be routed in/under floor joists (basement), then thru floor to panels (Buderus, bottom connection).
0 -
Would you still recommend coming thru the floor with copper pipe? It would be about 4-6" exposed. Or just run PEX up to the radiator and install the plastic covers that come with the panels?SWEI said:
The bottom connections work great with either 1/2" or 3/8" PEX. No worries about sagging like the top end pipe does.bmwpowere36m3 said:They'll be routed in/under floor joists (basement), then thru floor to panels (Buderus, bottom connection).
0 -
3/4 manifold viega if your running pex to each room might as well run a thermostate. With a bumble bee pump.0
-
Panel rads cry out for TRVs and delta P circsBob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream0 -
Ditto,HR is there really a better way?0
-
That's the plan…hot rod said:Panel rads cry out for TRVs and delta P circs
0 -
The latter, if I were doing it.bmwpowere36m3 said:
Would you still recommend coming thru the floor with copper pipe? It would be about 4-6" exposed. Or just run PEX up to the radiator and install the plastic covers that come with the panels?SWEI said:The bottom connections work great with either 1/2" or 3/8" PEX. No worries about sagging like the top end pipe does.
1
Categories
- All Categories
- 86.6K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 54 Biomass
- 423 Carbon Monoxide Awareness
- 98 Chimneys & Flues
- 2K Domestic Hot Water
- 5.5K Gas Heating
- 101 Geothermal
- 157 Indoor-Air Quality
- 3.5K Oil Heating
- 64 Pipe Deterioration
- 931 Plumbing
- 6.2K Radiant Heating
- 384 Solar
- 15.2K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 42 Industry Classes
- 48 Job Opportunities
- 17 Recall Announcements