Welcome! Here are the website rules, as well as some tips for using this forum.
Need to contact us? Visit https://heatinghelp.com/contact-us/.
Click here to Find a Contractor in your area.

Twintran tubing part of Entran II?

delta T
delta T Member Posts: 884
I have a customer that has Twintran installed in 1989, they are trying to sell the house and one of the inspection objections is the twintran tubing. The only stamp I can find is "UPC 2774 see boca research report number 87-51. Anyone have any idea if it is the dreaded Entran II? The install date is right, the color is right, but nowhere can I find a stamp that says Heatway on it, or Entran. Any help would be appreciated.

Thanks in advance!

Comments

  • hot_rod
    hot_rod Member Posts: 23,051
    Same basic product and it was included in the Goodyear Settlement

    Flush it, and isolate it with a HX is one common fix. If it becomes brittle and cracks, you're done. If it is in a slab it's tough to know if you have bad or brittle sections.
    Bob "hot rod" Rohr
    trainer for Caleffi NA
    Living the hydronic dream
  • delta T
    delta T Member Posts: 884
    Thank you, was looking for some confirmation, one way or the other. Greatly appreciated.