Ice on regulator...

kcopp
Member Posts: 4,520
in Gas Heating
Would a natural gas regulator on a meter be effected by a build up of ice on it either through a storm or otherwise? I always thought that this would make it work improperly... I was recently told by the local gas co meter installer that this would not be a problem.... Is that the same w/ LP gas?
ty,kcopp
ty,kcopp
0
Comments
-
The vent is the thing to look out for.......all gas regulators have a vent to atmosphere......and if they clog or freeze.....the diaphram will STICK in whatever it's position was exactly when it plugs or freezes. I KNOW WHAT I'M TALKING ABOUT.......I have seen 25psi inside a house from a frozen over regulator, and I have an 80-year old friend who is still working as a consultant for law enforcement, fire departments and insurance companies on natural gas and propane related fires and explosions. I taught the local gas codes licensing class for a while, and he brought in slide shows and talked to my students during every class.1
Categories
- All Categories
- 86.7K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 56 Biomass
- 423 Carbon Monoxide Awareness
- 104 Chimneys & Flues
- 2K Domestic Hot Water
- 5.6K Gas Heating
- 103 Geothermal
- 158 Indoor-Air Quality
- 3.5K Oil Heating
- 68 Pipe Deterioration
- 938 Plumbing
- 6.2K Radiant Heating
- 385 Solar
- 15.3K Strictly Steam
- 3.4K Thermostats and Controls
- 54 Water Quality
- 43 Industry Classes
- 47 Job Opportunities
- 18 Recall Announcements