Slant fin intrepid TR 30 boiler
LPM
Member Posts: 3
Slant fin steam boiler piping to manufacture specifications have a TR 30 boiler was piped with 2" header and 1"1/4 Hartford loop
I had surging and priming problems boiler was flooding
I read the slant fin TR 30 installation manual
And piped to manufacture specifications
3" steam header and 1"1/2 Hartford loop
Flushed and skim no more problems boiler working great
When talked to slant fin Rep (Perry)
I was told that good no more problems
But the header should be 2"1/2 and the Hartford loop 2"
Look at slant fin piping installation manual
It shows 3" header and 1"1/2 loop
I was told it could be a misprint
And would get back to me
If it's is an error shame on slant fin
I had surging and priming problems boiler was flooding
I read the slant fin TR 30 installation manual
And piped to manufacture specifications
3" steam header and 1"1/2 Hartford loop
Flushed and skim no more problems boiler working great
When talked to slant fin Rep (Perry)
I was told that good no more problems
But the header should be 2"1/2 and the Hartford loop 2"
Look at slant fin piping installation manual
It shows 3" header and 1"1/2 loop
I was told it could be a misprint
And would get back to me
If it's is an error shame on slant fin
0
Comments
-
Is this gas or oil? They have different specs depending. I always spoke to the technical support. I don't see a problem exceeding the minimum requirements; It can only help as you see.Two-pipe Trane vaporvacuum system; 1466 edr
Twinned, staged Slantfin TR50s piped into 4" header with Riello G400 burners; 240K lead, 200K lag Btus. Controlled by Taco Relay and Honeywell RTH6580WF0 -
It's Oil boiler0
-
The header has to be at least as large as the risers so with the recommended 3" riser you need AT LEAST a 3" header. I don't see how that can be wrong...they're very picky about their piping and wouldn't recommend downsizing the header from the riser. On my install of TR50s I used a 4" header. I think my HL is 2", but only because I kept and reused the original 2" iron piping. Their separate venting pdf is wrong, in that it's for the Galaxy atmospherics and not the Intrepids. I pointed it out last year...they agreed, but I see they haven't changed it. It's correct in the install manual.Two-pipe Trane vaporvacuum system; 1466 edr
Twinned, staged Slantfin TR50s piped into 4" header with Riello G400 burners; 240K lead, 200K lag Btus. Controlled by Taco Relay and Honeywell RTH6580WF0
Categories
- All Categories
- 86.6K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 54 Biomass
- 423 Carbon Monoxide Awareness
- 98 Chimneys & Flues
- 2K Domestic Hot Water
- 5.5K Gas Heating
- 101 Geothermal
- 157 Indoor-Air Quality
- 3.5K Oil Heating
- 64 Pipe Deterioration
- 931 Plumbing
- 6.2K Radiant Heating
- 384 Solar
- 15.2K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 42 Industry Classes
- 48 Job Opportunities
- 17 Recall Announcements