Gorton #C's vents not closing; Is there some 'prep' you are supposed to do?

Options
I have 10 radiators in my home. Most vents are Gorton 6's, but I have tried 2 #C's on the 2nd floor. In both cases the C's do not seem to close. They get stuck partially open until slightly jostled. 6's don't seem to have the same problem. Is there some "prep" one is supposed to do to break-in a vent so that it seats or closes better? Thanks.

Comments

  • Mark N
    Mark N Member Posts: 1,115
    Options
    I assume they are leaking steam. Have you tried rinsing them out. Might be some crud in the valve seat. What is your operating pressure? Gorton C's are a large valve, how big are the rads?
  • KC_Jones
    KC_Jones Member Posts: 5,739
    Options
    Agreed that is a large vent. I experimented with large rad vents and had some minor issues because of the steam rushing into the rad so fast, caused some spitting and the vent had difficulty closing. Switching to a slightly smaller vent eliminated the problem. Are you seeing any water spitting?
    2014 Weil Mclain EG-40
    EcoSteam ES-20 Advanced Boiler Control
    Boiler pictures updated 2/21/15
  • AJ_Marks
    AJ_Marks Member Posts: 15
    Options
    Yes. Definite spitting. The radiator is not large, because they are just 'steam convector radiators', but this pipe run seemed far enough for a #C. Sounds like if the #C is too big, it might "sweep up" crud or moisture which then cause it not to close (?)
  • Mark N
    Mark N Member Posts: 1,115
    edited January 2015
    Options
    Convectors need straight shank vents. Using a large vent like a C can cause imbalance in your steam distribution. The faster you vent a rad the higher the velocity of the steam in the riser. If the velocity is too high the condensate can't drain back causing all types of problems.
  • AJ_Marks
    AJ_Marks Member Posts: 15
    Options
    OK. Thanks for help. I'll downsize the C's to 6's.
  • Mark N
    Mark N Member Posts: 1,115
    edited January 2015
    Options
    Are you using straight shank vents? Also, a convector doesn't contain much air, a 6 might even be too large.
  • AJ_Marks
    AJ_Marks Member Posts: 15
    Options
    Yes. Straight shank, 1/4". I have 7 #6's and 1 #5. They seem to be doing fine. The 2 #C's were problems: splitting, not closing. I had previously swapped out 1 of them with a #6. But before I swapped out the other one, I thought I should check with HeatingHelp community to see if there was some "prep" or "break in" that I should have done with the valves. (all 10 vents in the system are newly replaced.)
  • KC_Jones
    KC_Jones Member Posts: 5,739
    Options
    Is all your main venting in proper order? You need to make sure the main venting is tuned before getting the radiation venting tuned in. In general you should start with small vents and then work up as necessary. Say #4 on first floor and then #5 for second floor as a baseline. After that if you find you need more heat in one room then you can increase the vent in that room. Did you happen to buy this? A lot of good information about venting in this eBook.
    http://store.heatinghelp.com/product-p/300.htm
    2014 Weil Mclain EG-40
    EcoSteam ES-20 Advanced Boiler Control
    Boiler pictures updated 2/21/15
  • AJ_Marks
    AJ_Marks Member Posts: 15
    Options
    Yes. Thanks. I did review e-book on venting with calcs. The mains are doing well. Given the pipe runs to the 2nd floor, a couple #C's had seemed good (based on e-Book and supported by info from Gorton.)