Slant Fin Won't Light All Burners
Steve_R
Member Posts: 5
I just finished my installation of my Slant Fin VHS-120. Did the LP conversion and changed orifices to 60's (I live at 8,000 ft elevation) When I get a call for heat, the blower comes on, pump comes on, pilot lights and proves, and the gas valve comes on. Usually only the burner rails near the pilot will light. Of 8 rails, usually only 4 will light. I seem to have good flame quality but I have to blow into the burn chamber to get the other burners to light. Once lit, they are fine. Other times I will give it a call for heat and all 8 burners light, no problem. I'm struggling with this one, and of course it's on my own house. Any help is appreciated! -Steve
0
Comments
-
Have you checked the gas pressure on both sides of the regulator (both off and when firing)?0
-
Did you change the regulator spring in the valve as well as the orifices.0
-
Unclejohn, I did change out the regulator spring in the LP conversion. SWEI, I haven't checked both sides yet. I find it strange that some times it lights, no problems at all. Other times it will only light 3 or 4 rails.0
-
Alright, I checked LP pressure and incoming was 13 3/4", manifold was only 6 1/4" so I turned it up to 9 1/2" as per the conversion specs. I still had trouble getting all the burners to light even with the increase in manifold pressure, so I started closing the shutters. Now, with the shutters a bit under 1/8" open, it lights all burners and fires fine. The conversion kit for this altitude came with #63 orifices. I also have #60's, so I wonder if I should put in the #60's?
0 -
I would get your LP CO. to come out and do a combustion test, It will be way worth the money.0
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 916 Plumbing
- 6K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements