Circulator Sizing - Help
GeorgeHC
Member Posts: 1
Will a B&G 2" circulator work properly and efficiently if installed on a one-pipe Monoflo diverter-tee system that has 1.25" main piping? The pump flanges and volute openings are 2", so I would be using a couple of reducers on the flanges to get this down to 1.25"
According to the pump curve, this pump is ideal for the required flow rate (10gpm) and head (10ft) that I have in this system. I'm just wondering if the reducers will create too much resistance and heat when the pump is running. This pump is brand new and free, so that's the only reason I am considering installing it. The current pump has a 1.5" volute and flanges, but is failing (motor and seal bearing assembly).
Thanks
According to the pump curve, this pump is ideal for the required flow rate (10gpm) and head (10ft) that I have in this system. I'm just wondering if the reducers will create too much resistance and heat when the pump is running. This pump is brand new and free, so that's the only reason I am considering installing it. The current pump has a 1.5" volute and flanges, but is failing (motor and seal bearing assembly).
Thanks
0
Comments
-
Yes, you should be able to get the appropriate flanges for it. What's the circ model?0
-
That pump is way too big. It will cause a lot of rushing water noise in the system and use way more electricity.
Sell it on eBay and use something like a Taco 0010.All Steamed Up, Inc.
Towson, MD, USA
Steam, Vapor & Hot-Water Heating Specialists
Oil & Gas Burner Service
Consulting0 -
Frank obviously knows what some here may not - that 2" is a model number for a specific three piece B & G circulator pump. It's a 1/6 HP three piece design with a curve that does indeed flow 10 GPM at 10 feet of head. That point lies at the left end of the curve. The other end is nearly 70 GPM at zero head.
The 008 curve gets very close to that point. The VT2218 nails it.0
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 916 Plumbing
- 6K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements