Old Moline vapor system boiler change out.
rws1443
Member Posts: 3
The boiler has been changed out and a condensate pump boiler feed unit added. Steam is coming back to the pump. What now?
rws1443
rws1443
0
Comments
-
I'd bet that condensate pump isn't needed. Many aren't. Steam is getting into the returns since they are no longer filled with water.
Post some pics of the boiler area so we can have a look. Also, where are you located?All Steamed Up, Inc.
Towson, MD, USA
Steam, Vapor & Hot-Water Heating Specialists
Oil & Gas Burner Service
Consulting0 -
I don't have access to get pictures. I was called in after the job. Being an industrial steam guy I put a trap ahead of the inlet to the receiver, that helped that problem, but I think it is going to cause others. I am in Denver, CO.
0 -
Moline systems are supposed to run at a pressure not exceeding 8 oz. Many folks often state 6 oz., but Moline documents say 8 oz. In addition, restriction rings on radiator supply valves and outlet valves are critical to regulate the right amount of steam to the radiator, thus keeping it from blowing through and into the return piping. If original valves have been replaced, or the slotted cylindrical restrictors have been removed (I've seen it!), the steam will blow right through and into the return piping. If this is the case, the easiest fix is to measure the EDR and order correct orifice plates (sized at 8 oz) from Tunstall. If the pressure at the boiler is exceeding 8 oz, it is likely that the boiler is oversized. A vaporstat is necessary to prevent pressure from exceeding 8 oz.
One thing with Moline Systems, and any fully orificed system for that matter, is that you do NOT have to allow for 34% piping and pickup factor, only a 15% piping loss factor, assuming that the mains are insulated and the amount of piping typical.
What kind of boiler are you running.... some Weil McLain LGB models come out of the factory with 2 stage capability and work great on Moline systems.Dave in Quad Cities, America
Weil-McLain 680 with Riello 2-stage burner, December 2012. Firing rate=375MBH Low, 690MBH Hi.
System = Early Dunham 2-pipe Vacuo-Vapor (inlet and outlet both at bottom of radiators) Traps are Dunham #2 rebuilt w. Barnes-Jones Cage Units, Dunham-Bush 1E, Mepco 1E, and Armstrong TS-2. All valves haveTunstall orifices sized at 8 oz.
Current connected load EDR= 1,259 sq ft, Original system EDR = 2,100 sq ft Vaporstat, 13 oz cutout, 4 oz cutin - Temp. control Tekmar 279.
http://grandviewdavenport.com5 -
Thanks, for the information. The contractor is running the system at 4 to 5 psig. He tells me that is the lowest pressure pressuretrol he can find. Any suggestions for the proper one would be greatly appreciated.0
-
Obviously that guy never heard of a Vaporstat.Hatterasguy said:
Remember the statement by Donald:rws1443 said:The contractor is running the system at 4 to 5 psig. He tells me that is the lowest pressure pressuretrol he can find. Any suggestions .................
"You're fired"
Use it.
All Steamed Up, Inc.
Towson, MD, USA
Steam, Vapor & Hot-Water Heating Specialists
Oil & Gas Burner Service
Consulting0 -
This is the device that is needed. http://www.supplyhouse.com/Honeywell-L408J1009-Vaporstat-Controller-Steam-0-to-16-oz-in2
Low pressure in this case, means atmospheric vapor. Pressure is SO low that it is almost nonexistent. The pressure is probably the main problem, perhaps its the only problem. If the contractor had installed a Vaporstat to start with, a condensate receiver and feedwater set up probably would not have been necessary as the condensate will flow back into the boiler by gravity at these low pressures.Dave in Quad Cities, America
Weil-McLain 680 with Riello 2-stage burner, December 2012. Firing rate=375MBH Low, 690MBH Hi.
System = Early Dunham 2-pipe Vacuo-Vapor (inlet and outlet both at bottom of radiators) Traps are Dunham #2 rebuilt w. Barnes-Jones Cage Units, Dunham-Bush 1E, Mepco 1E, and Armstrong TS-2. All valves haveTunstall orifices sized at 8 oz.
Current connected load EDR= 1,259 sq ft, Original system EDR = 2,100 sq ft Vaporstat, 13 oz cutout, 4 oz cutin - Temp. control Tekmar 279.
http://grandviewdavenport.com5
Categories
- All Categories
- 86.2K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 52 Biomass
- 422 Carbon Monoxide Awareness
- 89 Chimneys & Flues
- 2K Domestic Hot Water
- 5.3K Gas Heating
- 99 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 910 Plumbing
- 6K Radiant Heating
- 380 Solar
- 14.8K Strictly Steam
- 3.3K Thermostats and Controls
- 53 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements