Vacuum pump strange happening
Paul_11
Member Posts: 210
I did a steam survey recently on a two pipe vacuum system.
I had them shut the boiler down for three hours before I arrived.
When I turned the boiler back on, the vacuum pump immediately
had steam coming out of the vent pipe when the temperature
of the tank and of the condensate line feeding it was 85 degrees.
I don't see how this is possible, but I saw it with my own eyes.
Paul
I had them shut the boiler down for three hours before I arrived.
When I turned the boiler back on, the vacuum pump immediately
had steam coming out of the vent pipe when the temperature
of the tank and of the condensate line feeding it was 85 degrees.
I don't see how this is possible, but I saw it with my own eyes.
Paul
Since 1990, I have made steam systems quiet, comfortable, and efficient. We provide comfort while saving the planet.
NYC RETROFIT ACCELERATOR QUALIFIED SERVICE PROVIDER
A REAL GOOD PLUMBER, INC
NYC LMP: 1307
O:212-505-1837
M:917-939-0593
NYC RETROFIT ACCELERATOR QUALIFIED SERVICE PROVIDER
A REAL GOOD PLUMBER, INC
NYC LMP: 1307
O:212-505-1837
M:917-939-0593
0
Comments
-
The vacuum pump is usually equalized back to the pressure side of the system because it's possible to get a deeper vacuum on the radiator side of the radiator traps than the vacuum pump is producing at the time.. This often happens during the spring and fall when the system starts up and shuts down quickly. Without the equalizer, everything flows backwards when the radiator traps open. The equalizer breaks the vacuum and keeps this from happening. There's a check valve in that equalizer, and it's normally at the bottom of a U-tube pipe arrangement. If that's not in place, or if the check valve isn't holding, steam would have access from the boiler to the vacuum pump's receiver.
Retired and loving it.0 -
Is there a picture in either lost art or the companion to last art?
I'm trying to picture how this works, without getting steam into the vacuum pump which would destroy it.Since 1990, I have made steam systems quiet, comfortable, and efficient. We provide comfort while saving the planet.
NYC RETROFIT ACCELERATOR QUALIFIED SERVICE PROVIDER
A REAL GOOD PLUMBER, INC
NYC LMP: 1307
O:212-505-1837
M:917-939-05930 -
Lost Art on page 191 shows the equalizer used with a transfer pump and vacuum pump, but it would be the same with just the vacuum pump.Retired and loving it.0
-
Got it thanks.
Now I just have to think it through.
It looks like the steam equalizer line has a check valve aimed toward the steam header side.
So the equalizer would allow the higher pressure in the vacuum system to go into the steam side if it was in a deeper vacuum.
However, if that check valve is broken, the steam could flow right into the vacuum pump at all points of the heating cycle.
That could cause the issue I'm seeing.
However, if that equalizer line is not even there, it could not be causing this issue, but may cause another one later on under the right circumstances.
PaulSince 1990, I have made steam systems quiet, comfortable, and efficient. We provide comfort while saving the planet.
NYC RETROFIT ACCELERATOR QUALIFIED SERVICE PROVIDER
A REAL GOOD PLUMBER, INC
NYC LMP: 1307
O:212-505-1837
M:917-939-05930 -
Exactly.Retired and loving it.0
-
To be technically correct, the equalizer line doesn't break the vacuum, but equalizes the pressure between the steam side and the return side, which usually is still a pressure below atmosphere, AKA vacuum. Once the pressure is equalized, condensate can flow by gravity back to the receiver.
Sometimes these equalizer lines are fitted with a 3/4" thermostatic radiator trap an the end of an uncovered cooling leg, rather than the more common check valve arrangement Dan described.
Many times vacuum condensate return pump packages will have both a pressure vent line and a vacuum pump air discharge line. If live steam is coming out the pressure vent line, then you have live steam in the returns due to leaking trap(s) or defective equalizer line check valve. The reading on the compound gauge will be at zero, or slightly on the pressure side, depending on what the pressure actually is.
On the other hand, if you have what looks like steam discharging from the vacuum pump's air discharge line when the vacuum pump is running, this is moisture condensing out of the saturated air due to the temperature change from the returns to ambient air. The higher the discharged air temperature, the more moisture condenses out. Under these conditions, there will usually be a vacuum reading on the compound gauge.
I have never seen this happen with 85 degree condensate temperature.Dennis Pataki. Former Service Manager and Heating Pump Product Manager for Nash Engineering Company. Phone: 1-888 853 9963
Website: www.nashjenningspumps.com
The first step in solving any problem is TO IDENTIFY THE PROBLEM.0 -
Pumpguy,
Thanks so much for your insight.
I will be going back next year and taking a closer look.
I will most likely get back to you then.
I'm trying to get a hold of an installation manual for it and not having much luck.
Maybe you have it even though you rep nash jennings.
It is a varivac ventrite installed by G S Dunham.
Model # 178957
It has two condensate pumps and two vacuum pumps.
paul
Since 1990, I have made steam systems quiet, comfortable, and efficient. We provide comfort while saving the planet.
NYC RETROFIT ACCELERATOR QUALIFIED SERVICE PROVIDER
A REAL GOOD PLUMBER, INC
NYC LMP: 1307
O:212-505-1837
M:917-939-05930 -
Paul, check the Heating Museum. Lots there about the pumps: https://heatinghelp.com/assets/documents/dunham.pdf
It pays to wander.Retired and loving it.0 -
Paul,
I have good information on Dunham and Dunham - Bush / Mepco equipment, although this can get quite convoluted due to many changes with that product line over the years. Unfortunately the information you show does not come up in what I have, and may not now be tracable. This could have been a custom built unit. It would be best if I saw some pictures of this unit.
The information Dan posted shows dual purpose pumps that both pump condensate and also water through nozzle jets to produce the vacuum. Float controlled valves direct the water to the nozzle jets or the boiler as needed.
From your description, I suspect your unit has a pair of separate pumps for vacuum and another pair for condensate pumping purposes. I would need to see pictures to comment further.Dennis Pataki. Former Service Manager and Heating Pump Product Manager for Nash Engineering Company. Phone: 1-888 853 9963
Website: www.nashjenningspumps.com
The first step in solving any problem is TO IDENTIFY THE PROBLEM.0
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 917 Plumbing
- 6.1K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements