Beckett Aquasmart and Hydrolevel Fuel Smart HydroStat service

Options
GW
GW Member Posts: 4,692
Hello, we are starting to get service calls on the new Beckett Aquasmart; probe issues. Can any of you oil guys (that do this daily) comment on the pros and cons or general insights on these modern controls? Are you simply swapping out wells/sensors when the phone rings? Are you favoring the Hydrolevel?

Thanks for you comments.

Gary
Gary Wilson
Wilson Services, Inc
Northampton, MA
gary@wilsonph.com

Comments

  • Robert O'Brien
    Robert O'Brien Member Posts: 3,541
    Options
    There are issues with the 2n1 sensors that incorporate the LWCO. The standard temp only sensors and the AquaSmart control itself are fine. We have been temporarily replacing the 2n1 with temp only sensors until the situation is resolved.