got my Lochinvar whn85 today, found out it was built in 2011
Comments
-
Tim
Thank you very much for stepping up and saying your not sure now.I did call lockinvar again today, and spoke with another ajent, and she also said no changes have been made.
I think i will take the amount of money and keep the unit. I did try calling the manager at the distributo, went to voice mail, have not heard back from him yet
thanks again
Mark0 -
-
swei
thanks for the words of conffidence.
I won't find out until March or april, this is when my plumber will install the units.
Was it you that suggested the variable speed pumps? I have the 15-58, and i hope they will be fine, those variable speed pums are very expensive.
Me havingthe old converted gravity, would you suggest plumbing it full flow without a boiler loop, or the suggestion on 1 zone for sh 1 boiler loop and 1 priority for dhw?
thanks
mark0 -
-
swei
keep the dhw as priority? or a seperate zone? And would i wire the SH as a zone or the boiler loop?0 -
DHW priority is built in to the boiler. Some call it a zone, but the important thing is that it works and all you need is a pump with an IFC and you are good to go.0
-
Swei
what about wiring of the boiler and SH, do i put this on a zone?0 -
the pumps i purchased have flow checks0
-
Sorry -- what's SH?0
-
space heat0
-
If you're direct pumping it, they are one and the same. There's no 'zone' if you have only one pump, unless you have zone valves downstream of it.0
-
so hook it up to boiler pump? and hook it up to dhw pump?0
-
swei
what makes a single pump better for your system verses a loop and a system pump?0 -
swei
would keep my 25-58 st the slowest sppen then?0 -
Two pumps allow hydraulic separation of the boiler loop from the system loop. This allows maximum freedom for each with regards to flow rate and ΔT. It's absolutely required for some configurations. Others (like yours) with more forgiving characteristics sometimes allow the use of a simpler design. It's not trumpeted in their installation manuals because it only applies in specific cases -- and an unfortunate majority of installers in this day and age lack sufficient clue to be able to understand the difference.0
-
SweiI imagine what makes it good for me is that i have an old converted gravity fed system with alot of volumn of water. Is this correct?
The other question, how do i hook that 1 pump up, as a zone, or a boiler loop?
I also imagine, it will not affect dhw.
Will i need to do special piping for doing this system, or installing any other equiptment?
thanks
mark0 -
Again, I'm not really sure what you're asking here -- you need one pump for both the boiler and the system -- there are no 'zones' per se.0
-
swie
sorry if i'm not explaining myself well. I am refering to the wiring of this 1 pump for heat system and boiler, what does it get rired too in the electric panel0 -
Wire the circ to the System Pump terminals in the WH, then change the DHW Blocks Sys Pump parameter to NO. I would check with Lochinvar tech support to be sure there's not a similar blocking option for the Boiler Pump terminals, but I'm not aware of one.0
-
ok, thanks0
-
on the wire panel, dhw is priority.
I think I'm mixed up, thanks anyways0 -
Correct, the DHW pump gets wired to the DHW Pump terminals, and it has priority by default. I thought the system fired the boiler pump whenever there was a call of any kind, since they assume the use of primary/secondary piping. Now that I look at their diagrams again, they show the DHW piped in a way which seems to indicate that the boiler pump must not be running during a DHW call. No clear definition in the sequence of operation that I can see. I guess I need to give them a call on Monday to be certain.0
-
I think i get it now, this way, if I say no, durring the times that i don't need heat, and when i turn on the dwh, the other pump won't go on
I get it, this is all in the programing0
Categories
- All Categories
- 86.6K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 54 Biomass
- 423 Carbon Monoxide Awareness
- 97 Chimneys & Flues
- 2K Domestic Hot Water
- 5.5K Gas Heating
- 101 Geothermal
- 157 Indoor-Air Quality
- 3.5K Oil Heating
- 64 Pipe Deterioration
- 931 Plumbing
- 6.2K Radiant Heating
- 384 Solar
- 15.2K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 42 Industry Classes
- 48 Job Opportunities
- 17 Recall Announcements