here's a beauty

Options
Was at the local NAPA today and got to see this one,when its running sounds like someones back there with a ball-peen
hammer banging away.

Comments

  • Randy-LeeBraman
    Randy-LeeBraman Member Posts: 46
    Options
    Nope you can't,thank you Hatterasguy,i was hoping a few of the top steam members would comment on this.He has a tenant above the store who is always asking me if something could be done about the noise and the uneven heat,thought i could show
    some comments and maybe get it right.
  • Abracadabra
    Abracadabra Member Posts: 1,948
    Options
    LOL! I stopped counting how many things were wrong after counting fingers on one hand.
  • KC_Jones
    KC_Jones Member Posts: 5,739
    Options
    1. Colliding header (Main takeoff between risers).
    2. Equalizer not at the end of the header
    3. Bullhead tee on the mains (should be tied into header individually).
    4. Hartford loop appears to be a bit high, but that is hard to judge from a picture (I am looking at the LWCO for comparison).
    5. Mains are downsized
    6. And I am tired of typing....It just needs a complete re-pipe.
    How did they manage to make that riser connection on the side of the boiler back by the wall?! Why do people go to so much effort to do things wrong?
    2014 Weil Mclain EG-40
    EcoSteam ES-20 Advanced Boiler Control
    Boiler pictures updated 2/21/15