An Electrical Question
Harvey Ramer
Member Posts: 2,261
Is there any problem with running wires for a NTC thermistor, in the same conduit or cable as 24 volts AC?
0
Comments
-
Induced noise should be in the millivolts, and thermistors have a wide enough swing that the controller input circuitry should not even notice. A platinum RTD would be far more likely to see noise, but it could (should, actually) be filtered out by the controller.5
-
As long as your not drawing huge spikes of current and that cable is twisted pair you should be ok.
BobSmith G8-3 with EZ Gas @ 90,000 BTU, Single pipe steam
Vaporstat with a 12oz cut-out and 4oz cut-in
3PSI gauge5