Installing Gorton #2 on 3/4" main steam opening

The Gorton #2 (G2) appears to have only a 1/2 " size thread. The opening in my main is 3/4" is it possible to use the G2 or do i need to have multiple G1's which have a 3/4 " thread size into the main. I planned on connecting 2 G2's I would rather not do 6 G1's

Comments

  • Fred
    Fred Member Posts: 8,542
    Yes, you can use the Gorton #2. Just put them on a Tee and use a couple reducers to take you down to 1/2" and mount the Gortons.
    merikus
  • Don't they have 3/4 inch threads on the outside of the stem, as well as the 1/2 inch I.D.? that should give you a bit more flexibility.--NBC
  • Fred
    Fred Member Posts: 8,542
    Not the Gorton #2, just the #1's.
  • KC_Jones
    KC_Jones Member Posts: 5,840
    Fred said:

    Not the Gorton #2, just the #1's.

    And this somehow makes sense to Gorton...put bigger threads on the smaller vent. In reality it doesn't matter for venting capacity, but never made sense to me.
    2014 Weil Mclain EG-40
    EcoSteam ES-20 Advanced Boiler Control
    Boiler pictures updated 2/21/15
  • Fred
    Fred Member Posts: 8,542
    I could never understand their logic either