pump control question
varadhammo
Member Posts: 27
Hi all,
I'm in the process of figuring out the controls for my system. I have a tekmar 356 for injection mixing, grundfos alpha for the system pump. the zones are all radiant floor, with a combination of manifold actuators (2-wire no end switch) and zone valves. I have been planning on using a taco zvc zone valve control, but I realized that with the alpha autoadapt mode, it should just stay powered all the time and not be switched on and off by the ZVC. This leads me to think I could eliminate the ZVC altogether. But when there is a call for heat, I do need to trigger the 356 and the boiler primary pump. So is there a way I can somehow add a relay that will power the 356 injection controller and boiler pump based when the Alpha runs? I can't think of anything besides some kind of current sensing relay, but the power draw of the Alpha is so low that it probably wouldn't work properly. So any way to "detect" when the Alpha runs? Or does it make more sense to just use the ZVC and trigger the 356 & boiler pump from X-X? Thanks!
I'm in the process of figuring out the controls for my system. I have a tekmar 356 for injection mixing, grundfos alpha for the system pump. the zones are all radiant floor, with a combination of manifold actuators (2-wire no end switch) and zone valves. I have been planning on using a taco zvc zone valve control, but I realized that with the alpha autoadapt mode, it should just stay powered all the time and not be switched on and off by the ZVC. This leads me to think I could eliminate the ZVC altogether. But when there is a call for heat, I do need to trigger the 356 and the boiler primary pump. So is there a way I can somehow add a relay that will power the 356 injection controller and boiler pump based when the Alpha runs? I can't think of anything besides some kind of current sensing relay, but the power draw of the Alpha is so low that it probably wouldn't work properly. So any way to "detect" when the Alpha runs? Or does it make more sense to just use the ZVC and trigger the 356 & boiler pump from X-X? Thanks!
0
Comments
-
Wire the boiler terminals (#5 & 6) on the 356 to the boiler's TT terminals and let the internal pump relay on the boiler take care of the circ.0
-
My friend Nathan up in Alaska uses the Phenix model 9993 current sensing relay with ECM delta P circs. It senses from .1- 7 amp, around 25 bucks.Bob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream0 -
Hr, that looks perfect. Is he using it for something similar to what I described?hot rod said:My friend Nathan up in Alaska uses the Phenix model 9993 current sensing relay with ECM delta P circs. It senses from .1- 7 amp, around 25 bucks.
What I'm thinking is: current sensing relay on Alpha N.O. contacts close -> 356 mixing demand terminals & RIB dry contact relay to power primary circ at the GARN.0 -
Interesting idea. So the ECM circ becomes the demand indicator?0
-
Yes, exactly.0
-
Why not just let the internal Garn controls manage the primary circ?0
-
yes he has used that Phenix adjustable current sensing relay to fire tekmar controls with Wilo and Grundfos ECMs.Bob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream0 -
I'm planning on having the GARN primary circ wired to a RIB dry contact relay whose contacts will be closed by the GARN air intake damper end switch as well as the demands from the two buildings, so it will run whenever there's a heat demand and also whenever the GARN is charging (to provide a bit of extra tank mixing).
I'm not sure I understand what you mean... the Garn is just a storage tank sitting there, its controller just manages the batch burn, it doesn't respond to a call for heat in any way.SWEI said:Why not just let the internal Garn controls manage the primary circ?
0 -
I think the RIB folks offer them too, if you have access to that product line.
http://www.functionaldevices.com/building-automation/currentsensors.phpBob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream0 -
I thought Garn had at least some basic onboard controls (like a pump relay.) I'd probably suggest an aquastat to start the pump once the boiler actually heats up.
FDI has current sensors with power relays included -- see the lower third or so of the link above.0 -
It looks the RIB ones don't go down as low, only to .25A. What is the Alpha's lowest draw when it turns on? The Grundfos literature says low fixed speed ~ 5-8W which wouldn't even be 0.1A @ 120Vac... but maybe the pump wouldn't ever really run that low?0
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 64 Pipe Deterioration
- 918 Plumbing
- 6.1K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements