? about tridicator gauges
BigErl
Member Posts: 38
Hello everyone. When installing a tridicator gauge in the bull of a tee in a hydronic system do you want the probe in or out of the run of the tee?
0
Comments
-
Its best in the flow. Sometimes, if the bulb is too long, you can get it right with bushings and such.0
-
Thanks Icesailor.0