Review of Sorbox Elysator filter

Paul Pollets
Paul Pollets Member Posts: 3,656
The Sorbox has been on-line for over 3 weeks now. When we commissioned it, the boiler pH was at 6.2 and the conductivity was 268. Yesterday we tested the water and the pH had risen to 7.4 and the conductivity dropped to 202. The system is installed with a Vitodens 200 boiler in a 24 room dormitory. Corrosion had burned a hole through the 3 way mixing valve, despite O2 barrier tubing. Sorbox engineers said we did not have to add buffer solution to raise the pH...the unit would do so on its own. We're testing weekly to observe pH changes. I like what I see. So does the facility where the device was installed. They have 6 other boilers they'd like converted from chemical pot feeders to Sorbox units.