fields cas4 wiring

happydave
Member Posts: 79
Have a Burnham 204 that customer wants cas-4 , doesn't need but wants. Looking thru schematic and just can't figure where tt wiring goes into. Anyone have a simple drawing how it's wired into system.
0
Comments
-
Theres a number of scenarios, which one do you have?
You're probably page 8, figure 8
http://www.fieldcontrols.com/pdfs/46284600.pdfThere was an error rendering this rich post.
0 -
Steve , page8 is it but do I just splice into the red and white off the vent damper?0
-
No, splice implies stripping the insulation, and tying all 3 wires together. Note the dotted lines (wire supplied by you)
In reality you would remove the red/white from the vent damper and run the 2 wires to the T1 & T2 on the wiring block. Then get another 2 wire and run it from T2 & T3 on the block to the ignition module TR & TH respectively.There was an error rendering this rich post.