Weil-McLain Ultra Series 3 MAWP?

Options
JohnNY
JohnNY Member Posts: 3,231
Does anyone know the max working pressure of a WM Ultra Series 3CT?

I can't find it online and I have a client asking me to put one in the cellar of a 6-story building.

Contact John "JohnNY" Cataneo, NYC Master Plumber, Lic 1784
Consulting & Troubleshooting
Heating in NYC or NJ.
Classes

Comments

  • icesailor
    icesailor Member Posts: 7,265
    Options
    If you figure a minimum of 10' per floor, that's 60' if the boiler is in a basement and the top floor radiation is 60' above the boiler, that equals 26# PSI. Not a lot of wiggle room in the system.
  • JohnNY
    JohnNY Member Posts: 3,231
    Options
    abracadabra, are you sure that's for the Series 3?
    I could've sworn I'd heard that the newest Ultra would allow a higher mawp.

    Thanks a lot.

    Contact John "JohnNY" Cataneo, NYC Master Plumber, Lic 1784
    Consulting & Troubleshooting
    Heating in NYC or NJ.
    Classes
  • RobG
    RobG Member Posts: 1,850
    Options
    You could look at the HydroTherm KN series boilers, they are rated at 100 psi. I think Wales Darby is the rep for NY.
  • SWEI
    SWEI Member Posts: 7,356
    Options
    We have a system running about as close to the limits of a 30# relief valve as one can get. System height is 54 feet and it's running at 28-29 PSI. Boiler pumps on the 399's pump away from the boilers (firetube HX) to prevent the relief valves from burping on the differential pressure.
  • Abracadabra
    Abracadabra Member Posts: 1,948
    Options
    JohnNY said:

    abracadabra, are you sure that's for the Series 3?
    I could've sworn I'd heard that the newest Ultra would allow a higher mawp.

    Thanks a lot.

    yeah.. pretty sure.. the relief valve they supply with it is still a 30psi. docs for the series 3 say 30psi.

  • RobG
    RobG Member Posts: 1,850
    Options
    A little off topic but why don't manufacturers test their boilers for higher working pressure? If HydroTherm can do it, why can't others? I used to use the HydroTherm modular boilers quite a bit and they were 75psi.
  • BobC
    BobC Member Posts: 5,479
    Options
    I'll bet higher pressures mean you have to use more lawyer repellant and we all know how expensive that is!

    Bob
    Smith G8-3 with EZ Gas @ 90,000 BTU, Single pipe steam
    Vaporstat with a 12oz cut-out and 4oz cut-in
    3PSI gauge
  • Rich_49
    Rich_49 Member Posts: 2,766
    Options
    Johnny , this has an 80 PSI MWP for the 285 and 399 units .
    Click specifications , this is available where you are also .

    http://www.htproducts.com/commercial-eft-documents.html

    You didn't get what you didn't pay for and it will never be what you thought it would .
    Langans Plumbing & Heating LLC
    732-751-1560
    Serving most of New Jersey, Eastern Pa .
    Consultation, Design & Installation anywhere
    Rich McGrath 732-581-3833
  • JohnNY
    JohnNY Member Posts: 3,231
    edited November 2014
    Options
    Thanks, guys. Rich, I'll look again at the HTP but I'm enjoying the Lochinvar line at the moment. The Knight XL is certified at 160psi and I like the control interface and customer support I get (hello, Jerry Katz) at Wallace-Eannace.

    I've got a client asking for the Ultra, it happens a lot so I accommodate, and I'm checking to see if it's compatible with the conditions.
    I guess it isn't.
    Contact John "JohnNY" Cataneo, NYC Master Plumber, Lic 1784
    Consulting & Troubleshooting
    Heating in NYC or NJ.