Weil-McLain Ultra Series 3 MAWP?

JohnNY
JohnNY Member Posts: 3,308
Does anyone know the max working pressure of a WM Ultra Series 3CT?

I can't find it online and I have a client asking me to put one in the cellar of a 6-story building.

Contact John "JohnNY" Cataneo, NYC Master Plumber, Lic 1784
Consulting & Troubleshooting
Heating in NYC or NJ.
Classes

Comments

  • icesailor
    icesailor Member Posts: 7,265
    If you figure a minimum of 10' per floor, that's 60' if the boiler is in a basement and the top floor radiation is 60' above the boiler, that equals 26# PSI. Not a lot of wiggle room in the system.
  • JohnNY
    JohnNY Member Posts: 3,308
    abracadabra, are you sure that's for the Series 3?
    I could've sworn I'd heard that the newest Ultra would allow a higher mawp.

    Thanks a lot.

    Contact John "JohnNY" Cataneo, NYC Master Plumber, Lic 1784
    Consulting & Troubleshooting
    Heating in NYC or NJ.
    Classes
  • RobG
    RobG Member Posts: 1,850
    You could look at the HydroTherm KN series boilers, they are rated at 100 psi. I think Wales Darby is the rep for NY.
  • SWEI
    SWEI Member Posts: 7,356
    We have a system running about as close to the limits of a 30# relief valve as one can get. System height is 54 feet and it's running at 28-29 PSI. Boiler pumps on the 399's pump away from the boilers (firetube HX) to prevent the relief valves from burping on the differential pressure.
  • Abracadabra
    Abracadabra Member Posts: 1,948
    JohnNY said:

    abracadabra, are you sure that's for the Series 3?
    I could've sworn I'd heard that the newest Ultra would allow a higher mawp.

    Thanks a lot.

    yeah.. pretty sure.. the relief valve they supply with it is still a 30psi. docs for the series 3 say 30psi.

  • RobG
    RobG Member Posts: 1,850
    A little off topic but why don't manufacturers test their boilers for higher working pressure? If HydroTherm can do it, why can't others? I used to use the HydroTherm modular boilers quite a bit and they were 75psi.
  • BobC
    BobC Member Posts: 5,511
    I'll bet higher pressures mean you have to use more lawyer repellant and we all know how expensive that is!

    Bob
    Smith G8-3 with EZ Gas @ 90,000 BTU, Single pipe steam
    Vaporstat with a 12oz cut-out and 4oz cut-in
    3PSI gauge
  • Rich_49
    Rich_49 Member Posts: 2,773
    Johnny , this has an 80 PSI MWP for the 285 and 399 units .
    Click specifications , this is available where you are also .

    http://www.htproducts.com/commercial-eft-documents.html

    You didn't get what you didn't pay for and it will never be what you thought it would .
    Langans Plumbing & Heating LLC
    732-751-1560
    Serving most of New Jersey, Eastern Pa .
    Consultation, Design & Installation anywhere
    Rich McGrath 732-581-3833
  • JohnNY
    JohnNY Member Posts: 3,308
    edited November 2014
    Thanks, guys. Rich, I'll look again at the HTP but I'm enjoying the Lochinvar line at the moment. The Knight XL is certified at 160psi and I like the control interface and customer support I get (hello, Jerry Katz) at Wallace-Eannace.

    I've got a client asking for the Ultra, it happens a lot so I accommodate, and I'm checking to see if it's compatible with the conditions.
    I guess it isn't.
    Contact John "JohnNY" Cataneo, NYC Master Plumber, Lic 1784
    Consulting & Troubleshooting
    Heating in NYC or NJ.
    Classes