How to remove steam radiator valve
yafirst
Member Posts: 3
We bought a house recently and one of the radiators is always cold. We tried to remove it to clean, but we haven't been able to remove the valve: it's stuck. I'd appreciate any tips on how it can be removed. Thank you in advance for all help.
0
Comments
-
-
Either that, or this radiator is all the way at the end of the main, and the main vent is either missing or too small.All Steamed Up, Inc.
Towson, MD, USA
Steam, Vapor & Hot-Water Heating Specialists
Oil & Gas Burner Service
Consulting0 -
Stand about 5 or 6 feet away and give a photo of the entire radiator. Top to bottom and one end to the other. Including pipe connections.0
-
Before going any further with that nut I would follow the suggestions above and look underneath to see if the piping has the correct slope so water can find it's way back to the boiler.
That valve looks like it's been there a long time and it probably has multiple coats of paint sealing it pretty good. if you get too rambunctious you could snap that nut. Have you tried rapping the nut with ball peen to see if vibration might free it?
BobSmith G8-3 with EZ Gas @ 90,000 BTU, Single pipe steam
Vaporstat with a 12oz cut-out and 4oz cut-in
3PSI gauge0 -
We've changed the air vent: it didn't help. Same story with the ball pen. Here is another picture. Thank you everyone!0
-
Bob, I am also thinking that the multiple coats of paint prevent us from moving the nut. Is there a trick to remove all this paint?0
-
Have you tried tightening that nut, sometimes that works to break the seal? Then you could probably back it off.
Anything that would remove that paint would ruin the rug and the wall.
BobSmith G8-3 with EZ Gas @ 90,000 BTU, Single pipe steam
Vaporstat with a 12oz cut-out and 4oz cut-in
3PSI gauge0 -
-
Same first thought I had, I don't see one either.Paul48 said:Where's the vent on that radiator? I don't see it in the picture.
0 -
The radiator is pitched. Someone probably removed the vent because it leaked.0
-
It probably has a water system vent on it, and needs a proper one pipe system radiator vent.--NBC0
-
Paul48 said:
Where's the vent on that radiator? I don't see it in the picture.
Ding.. ding.. ding... we have a winner! Funny thing is the OP said they changed the vent. I'm wondering now what they actually replaced.KC_Jones said:
Same first thought I had, I don't see one either.Paul48 said:Where's the vent on that radiator? I don't see it in the picture.
0 -
Probably went to HD with the old one and they gave them a coin vent to replace it with. The Sales Representative thinks that steam is a by-product of boiling water in a pot on the stove.
And steam venting devices are far more money than a coin vent.0 -
I'd almost bet they are turning the union nut backwards.0
-
Judging by the fact that there is no paint on the packing nut, I'll bet someone has futzed with in the past.
When the steam pressure is off, back off the nut, all the way out, and give it the Kroil Treatment. Once the stem loosens up, there is probably nothing wrong with the valve. And a lack of an air vent.1 -
Would it be possible to get a photo of the new air vent on the radiator? Perhaps it's a trick of the light, but as others have said, it seems that there's no air vent, at least of the traditional sort. Typical steam systems require air vents on the mains and the radiators to let cold air out so that it can be displaced by the steam coming up from the boiler; without a working air vent on the side of the radiator opposite the steam pipe, cold air will just sit in the radiator and laugh at the steam trying to get in.
Also, how far is this radiator from the boiler? Depending on distance from the boiler and rate at which the vent can let air out, it's possible that the thermostat is satisfied before steam can reach the radiator.
0 -
Call a plumber if you cant open union.If you are feeling adventerous and union wont open with a wrench you can open it with a hammer.Hit the knuckle of the union with hammer and it will open dont be afraid to hit it.0
Categories
- All Categories
- 86.5K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 423 Carbon Monoxide Awareness
- 94 Chimneys & Flues
- 2K Domestic Hot Water
- 5.5K Gas Heating
- 101 Geothermal
- 156 Indoor-Air Quality
- 3.5K Oil Heating
- 64 Pipe Deterioration
- 925 Plumbing
- 6.1K Radiant Heating
- 383 Solar
- 15.1K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 48 Job Opportunities
- 17 Recall Announcements