Hydrolevel Safgard LWCO's (mod 400)
Robert O'Connor_12
Member Posts: 728
Anyone experiencing these controls NOT shutting down boiler on low water? So far, I had three in less than a month. Most recent, on a brand new Thermoflo.
Also, some that do work initially aren't "playing well" with water feeders.
thoughts.....?
Also, some that do work initially aren't "playing well" with water feeders.
thoughts.....?
0
Comments
-
Only thing that comes to mind is I've heard using too much sealer on the threads of the probe can cause problems, but I don't know what kind of problems.
Single pipe 392sqft system with an EG-40 rated for 325sqft and it's silent and balanced at all times.
0 -
packaged boiler.
took the probe(s) out & cleaned them. I don't use Teflon tape or paste on them either. I typically use the grey dope when replacing them.0 -
only pipe dope on probe, teflon on probe blocks grounding the probe and will not work0