Welcome! Here are the website rules, as well as some tips for using this forum.
Need to contact us? Visit https://heatinghelp.com/contact-us/.
Click here to Find a Contractor in your area.

Hydrolevel Safgard LWCO's (mod 400)

Anyone experiencing these controls NOT shutting down boiler on low water? So far, I had three in less than a month. Most recent, on a brand new Thermoflo.
Also, some that do work initially aren't "playing well" with water feeders.
thoughts.....?

Comments

  • ChrisJ
    ChrisJ Member Posts: 16,231
    Only thing that comes to mind is I've heard using too much sealer on the threads of the probe can cause problems, but I don't know what kind of problems.
    Single pipe quasi-vapor system. Typical operating pressure 0.14 - 0.43 oz. EcoSteam ES-20 Advanced Control for Residential Steam boilers. Rectorseal Steamaster water treatment
  • Robert O'Connor_12
    Robert O'Connor_12 Member Posts: 728
    packaged boiler.
    took the probe(s) out & cleaned them. I don't use Teflon tape or paste on them either. I typically use the grey dope when replacing them.
  • gcp13
    gcp13 Member Posts: 122
    only pipe dope on probe, teflon on probe blocks grounding the probe and will not work